[RE-wrenches] MC4 Y Connectors
conrad geyser
conradg at cape.com
Wed Mar 7 07:42:58 PST 2012
Allen,
Our read is that it's OK to use unfused wyes on systems with 2 strings only.
If one string shorts, the other string can't overcurrent it. As soon as you
are ringing together more than two strings, you need to fuse each one.
Conrad
Cotuit Solar