That might be ok for a system with only two strings.

For systems with more than two, it would likely overload the series 
fuses, depending on their rating compared to module output.

At 04:35 AM 3/7/2012, you wrote:
>Wrenchers,
>Has anyone used MC4 Y Connectors to combine strings?  This website 
>claims that they are TUV Certified but does not list the 
>manufacturer.  Seems like best practice to fuse each string but 
>wanted to see what others think about this product and the idea of 
>fusing every two strings instead of each individual string.
>
><http://www.solarpenny.com/MC4-Y-Connectors-609-4431.htm>http://www.solarpenny.com/MC4-Y-Connectors-609-4431.htm
>
>Al Frishman
>AeonSolar
>
><tel:%28917%29%20699-6641>(917) 699-6641 - cell
><tel:%28888%29%20460-2867>(888) 460-2867
><http://www.aeonsolar.com/>www.aeonsolar.com
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org

Drake Chamberlin
ATHENS ELECTRIC LLC
OH License 44810
CO license 3773
NABCEP Certified PV
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120307/0350e047/attachment-0004.html>


More information about the RE-wrenches mailing list