Daryl:
By chance, is there a Flex Net that is also tied into this system? Though I
love the idea of having SOC parameters built into the AGS, I have nothing
but problem with them. Especially with older battery banks, they seem to
want to start either a 2 hour, or 2 minute timer, regardless of the voltage
or SOC. If you do have a Flexnet in the system, I would disconnect it from
the battery and the hub and restart the system without it. Then at least you
can tweak the voltage parameters and timers to solve the issue.