[RE-wrenches] meter pan?

Alex Cozine acdc.cozine at gmail.com
Tue Jan 24 23:37:27 PST 2012


In some areas in Washington no outside disconnect is required for
production meter when under 5kw system.

On Tue, Jan 24, 2012 at 10:30 AM, Isaac Opalinsky <iopalinsky at gmail.com>wrote:

> The funny thing about requiring a disconnect on both sides of the meter is
> that the meter is only energized from one source - the utility.  And for
> that matter, 230.82 permits a meter to be on the supply side of a service
> disconnect (it sounds like you were proposing the meter would be on the
> load side of the PV System Disconnect).  Anything having to do with the
> arrangement between a meter and a disconnect (or disconnects) is either a
> local amendment, utility requirement or an incentive program requirement.
>  Couldn't you even have a meter with no disconnect (as far as the NEC is
> concerned)?
>
> Isaac Opalinsky
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Alex Cozine
NABCEP Certified Solar PV Installer™
Journeyman Electrician

Brothers Electric & Solar
brotherselectricsolar.com