[RE-wrenches] Point of Connection 705.12D2 Exception

John Berdner John.Berdner at solaredge.com
Sun Dec 30 13:54:17 PST 2012


Jeremy:

31.25 is the minimum allowable Ampacity (25 Amps continuous) so a 35 Amp breaker would be the minimum size per Code.
The inverter may have a higher "pass through rating" to support the loads and so is likely the reason a 60 Amp breaker is specified.
The pass through rating is typically based on the size of the isolation relay and is usually higher than the inverter's continuous power rating.

Best Regards,

John Berdner
General Manager, North America



3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new address.)
T: 510.498.3201 ext 747
M: 530.277.4894

-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jeremy Rodriguez- All Solar Inc.
Sent: Sunday, December 30, 2012 10:35 AM
To: re-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] Point of Connection 705.12D2 Exception

Wrenches,
Since the XW6048 calls for a 60A breaker to feed the inverter input and we are connecting back to the load side of a 200A panel is this correct. 6000÷240=25X1.25=31.25A. We cannot exceed a 30A breaker?  Help me understand this.
Jeremy
All Solar
Sent via BlackBerry. Sorry for typos and shorthand!
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for the use of the individual or entity who is the intended recipient and may contain information that is privileged, confidential and exempt from disclosure or any type of use under applicable law. If the reader of this e-mail is not the intended recipient, or the employee, agent, or representative responsible for delivering the e-mail to the intended recipient, you are hereby notified that any dissemination, distribution, copying, or other use of this e-mail is strictly prohibited. If you have received this e-mail in error, please reply immediately to the sender.
P Please think of the environment before printing this email



More information about the RE-wrenches mailing list