[RE-wrenches] Point of Connection 705.12D2 Exception

Jeremy Rodriguez- All Solar Inc. allsolar at scswifi.net
Sun Dec 30 10:35:00 PST 2012


Wrenches,
Since the XW6048 calls for a 60A breaker to feed the inverter input and we are connecting back to the load side of a 200A panel is this correct. 6000÷240=25X1.25=31.25A. We cannot exceed a 30A breaker?  Help me understand this. 
Jeremy
All Solar
Sent via BlackBerry. Sorry for typos and shorthand!