[RE-wrenches] Remote relay options

Chris Mason cometenergysystems at gmail.com
Sun Dec 9 15:16:00 PST 2012


Then you have to find a 600V DC rated contactor. If you are going to use a
contactor, which the original poster said he couldn't do, why not use the
240V AC rated, costs about $129 for a 30A contactor.


On Sun, Dec 9, 2012 at 6:10 PM, Drake
<drake.chamberlin at redwoodalliance.org>wrote:

> Why not disconnect the DC into the inverter with a Tyco relay?  No DC, no
> AC.
>
>
>
>
> At 10:32 AM 12/5/2012, you wrote:
>
>> Hi All,
>>
>> I am looking for options for controlling a disconnecting relay for a
>> grid-tied inverter.  It is a PVI5000 so 30 amp 240vAC.  I need to
>> disconnect it when the backup generator gets kicked on by the Automatic
>> Transfer Switch when the grid goes down.  The array is on a garage that is
>> several hundred feet from the house and service entrance and ATS and
>> digging in a control wire for that distance won't work.  So I need a way
>> to sense that the generator is putting out power and then control a
>> contactor which would disconnect the inverter from the subpanel.  I've
>> looked for wireless and powerline control options but I can't seem to put
>> together the pieces.
>>
>> Any ideas of the most cost effective and reliable approach?
>>
>> Thanks,
>> Howie
>> --
>> Howie Michaelson
>> NABCEP Certified Solar PV Installer™
>>
>> Catamount Solar, LLC
>> Renewable Energy Systems Sales and Service
>> VT Solar Electric & Hot Water Incentive Partner
>> http://www.CatamountSolar.com
>> 802-272-0004
>>
>>
>>
>>
>>
>> ______________________________**_________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.**org<RE-wrenches at lists.re-wrenches.org>
>>
>> Options & settings:
>> http://lists.re-wrenches.org/**options.cgi/re-wrenches-re-**wrenches.org<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>
>> List-Archive: http://lists.re-wrenches.org/**pipermail/re-wrenches-re-**
>> wrenches.org<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.**htm<http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>
> ______________________________**_________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.**org<RE-wrenches at lists.re-wrenches.org>
>
> Options & settings:
> http://lists.re-wrenches.org/**options.cgi/re-wrenches-re-**wrenches.org<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>
> List-Archive: http://lists.re-wrenches.org/**pipermail/re-wrenches-re-**
> wrenches.org<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.**htm<http://www.re-wrenches.org/etiquette.htm>
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20121209/343625ad/attachment-0003.html>


More information about the RE-wrenches mailing list