[RE-wrenches] Remote relay options

Drake drake.chamberlin at redwoodalliance.org
Sun Dec 9 14:10:03 PST 2012


Why not disconnect the DC into the inverter with a Tyco relay?  No DC, no AC.



At 10:32 AM 12/5/2012, you wrote:
>Hi All,
>
>I am looking for options for controlling a disconnecting relay for a
>grid-tied inverter.  It is a PVI5000 so 30 amp 240vAC.  I need to
>disconnect it when the backup generator gets kicked on by the Automatic
>Transfer Switch when the grid goes down.  The array is on a garage that is
>several hundred feet from the house and service entrance and ATS and
>digging in a control wire for that distance won't work.  So I need a way
>to sense that the generator is putting out power and then control a
>contactor which would disconnect the inverter from the subpanel.  I've
>looked for wireless and powerline control options but I can't seem to put
>together the pieces.
>
>Any ideas of the most cost effective and reliable approach?
>
>Thanks,
>Howie
>--
>Howie Michaelson
>NABCEP Certified Solar PV Installer™
>
>Catamount Solar, LLC
>Renewable Energy Systems Sales and Service
>VT Solar Electric & Hot Water Incentive Partner
>http://www.CatamountSolar.com
>802-272-0004
>
>
>
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org




More information about the RE-wrenches mailing list