[RE-wrenches] PV String Over-voltage
Benn At DayStarSolar
benn at daystarsolar.ca
Thu Nov 29 20:23:18 PST 2012
Larry,
Would it not be a more straightforward approach to just size the strings, temperature compensating for the coldest anticipated temp?
Nonetheless, such a device could be useful in some circumstances. I'd be interested to know if your search comes up with something.
benn
Sent from a 'smart' phone, with touch screen keys. Please excuse shortcuts and typos.
On 2012-11-29, at 6:53 PM, "Larry Crutcher, Starlight Solar Power Systems" <larry at starlightsolar.com> wrote:
> Wrenches,
>
> I seem to recall seeing something about a device for PV string over-voltage protection by bypassing a module. I can't find any info by Goggling.
>
> Some customers in the FAR north, ay, can see > 40° below zero with bright sun and snow reflection. I want to be able to switch off one or more modules in a string for protecting the controllers.
>
> Thank you,
>
> Larry Crutcher
> Starlight Solar Power Systems
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20121129/17c69c69/attachment-0003.html>
More information about the RE-wrenches
mailing list