JASON:
I talked to Steve Capozzi of SolaDeck and he sent me additional info
about the circuit breakers:
_Manufacturer_: ABB
_Terminal Temp Rating_: 75C / 167F
_Reference Temperature_: 20C / 68F
_Ambient Temp Derating_:
30C/86F = 18.7A
40C/104F = 17.3A
50C/122F = 15.8A
60C/140F = 14.1A
70C/158F = 12.2A
My concern is that we may be attempting to use an interior rated AC
breaker in a roof-deck-mounted NEMA3-R enclosure.
In an Enphase application, with the maximum of 17 inverters per AC
Source Circuit, the continuous current will be 0.9A x 17 x 1.25 = 19.1A.
This exceeds the 30C/86F trip current of 18.7A.
The interior temperature of the SolaDeck could very likely approach the
60C/140F trip current of 14.1A.
It seems to me that "nuisance trips" could be a high probability event.
Does anyone have any field experience using this Soladeck option for a
AC Source Circuit Combiner Box (SCCB)?
Another issue, at least in some jurisdictions, is the requirement for a
roof-top AC Disconnect.
The SolaDeck, when used as an AC SCCB, may not meet the NEC Article 100
requirements in some jurisdictions for "readily accessible" because a
tool is required to open it.
Regards,
Gary Willett, PE
Icarus Engineering LLC
Icarus Solar Services LLC
On 11/26/2012 2:21 PM, Jason Szumlanski wrote:
> I did get some pictures and info from Soladeck. Here are some links:
>
> Pics:
> https://docs.google.com/open?id=1BpiL-1SdSNNsj4wPMQrFCLHH7JT2dek_KftSJl06QLqc0yhJ_1t5oij0aEA6
> https://docs.google.com/open?id=1cVuhZGeQNHL1IvGvNBa7v93oZyGBvjxCv5yq4AmoyJeDAITxvgMqgECR2yTv
> https://docs.google.com/open?id=1umslTplnFyZG1eNCZE-MMi_OqrSeirFCPRBl9mFNZJ2gQkBjM5LEXnaPKy2l
> Specs:
> https://docs.google.com/open?id=13KLAuxUHOR9al7-36reDSJJ7IMnqV3ANPnJILPnrj2xcAi0ksRj67ifKIe7R
> https://docs.google.com/open?id=1kvPFcDc1vruS3W_aONlXyIHm1T8-qi4vTpTwGGJ7H0eIwuZ-5e6zrM1CcND5
> https://docs.google.com/open?id=1lM8FtYl9HiYohru32UA_Gb1tXZKZ5iw-8tnSu1Un6g4vcklLL-DK1qLPMdsB
>
> I was told Soligent can source the combiners for you (and me).
>
> *Jason Szumlanski*//
>
> /Fafco
> Solar/<http://www.wisestamp.com/apps/wordpress?utm_source=extension&utm_medium=email&utm_term=wordpress&utm_campaign=apps>
>
>
> On Mon, Nov 26, 2012 at 1:50 PM, Jason Szumlanski
> <jason at fafcosolar.com <mailto:jason at fafcosolar.com>> wrote:
>
> I just called Soladeck and they are sending me some more info on
> availability. I'll pass it along when I get it. I didn't realize
> they made an AC roof mounted string combiner solution. That's a
> huge help for 2 or 3 string Enphase installations (they make both
> combiners).
>
> While on the subject, we recently started using the Enphase cable
> couple with Type TC-ER cable to extend cabling to junction boxes
> when necessary... No more wasting trunk cable connectors! I
> suppose Type TC-ER could be used all the way to the main
> distribution panel, thereby eliminating junctions on the roof, but
> I haven't looked into the cost/benefit of that idea.
>
> *Jason Szumlanski*
>
> /Fafco Solar/
>
>
>
> On Mon, Nov 26, 2012 at 1:26 PM, Gary Willett
> <gary at icarussolarservices.com
> <mailto:gary at icarussolarservices.com>> wrote:
>
> NICK:
>
> I could not find the AC model numbers you provided on the
> SolaDeck web site. Do you know the manufacturer, and the
> voltage and temperature ratings, for the 2-pole 20A AC breakers?
>
> Regards,
>
>
> Gary Willett, PE
> Icarus Engineering LLC
>
> Icarus Solar Services LLC
>
>
> On 11/26/2012 11:54 AM, Nick Soleil wrote:
>> Hi wrenches;
>>
>> SolaDeck Models 0760-41AD and 0766-41AD are rated for up to
>> 60A at 240Vac.
>>
>> It can be ordered with DIN rail mounted AC breakers and a
>> combiner kit. The 2 - 20A circuit combiner kit is part 0760K2AC.
>>
>> I'd recommend checking with a distributor or on SolaDeck's
>> website for the most current information.
>>
>> Nick Soleil,
>> Enphase Energy
>>
>>
>> On Sun, Nov 25, 2012 at 7:44 AM, Kent Osterberg
>> <kent at coveoregon.com <mailto:kent at coveoregon.com>> wrote:
>>
>> My understanding has been that the Soladeck has only been
>> listed for DC wiring. Perhaps they have a manufacturer
>> rep on RE-wrenches that can clarify.
>>
>> Kent Osterberg
>> Blue Mountain Solar, Inc.
>> www.bluemountainsolar.com <http://www.bluemountainsolar.com>
>>
>>
>>
>> On 11/25/2012 6:20 AM, Dave Palumbo wrote:
>>
>> Rich,
>>
>> We have been using SolaDeck PV roof mount enclosure.
>> NEMA 3R with a flashed
>> penetration. Can use for combining, or simply as a
>> pass through box.
>>
>> Dave
>>
>> David Palumbo
>> Independent Power LLC
>> 462 Solar Way Drive
>> Hyde Park, VT 05655
>> www.independentpowerllc.com
>> <http://www.independentpowerllc.com>
>> NABCEP Certified PV Installer
>> Vermont Solar Partner
>> 25 Years Experience, (802) 888-7194
>> <tel:%28802%29%20888-7194>
>>
>>
>>
>>
>> -----Original Message-----
>> From: re-wrenches-bounces at lists.re-wrenches.org
>> <mailto:re-wrenches-bounces at lists.re-wrenches.org>
>> [mailto:re-wrenches-bounces at lists.re-wrenches.org
>> <mailto:re-wrenches-bounces at lists.re-wrenches.org>]
>> On Behalf Of Rich Nicol
>> Sent: Sunday, November 25, 2012 8:11 AM
>> To: 'RE-wrenches'
>> Subject: [RE-wrenches] Best practices for conduit
>> penetration on roof
>>
>> Wrenches,
>> We typically run conduit for roof mounts over the
>> edge of the roof to the
>> eaves, rather than penetrate the roof whenever
>> possible. An upcoming
>> installation on an freshly asphalt shingled roof
>> requires that we penetrate
>> the roof for the conduit run (Enphase). I'm wondering
>> if there are any
>> suggestions for preferred flashing products and best
>> known practices. It's
>> always seemed to me that the typical Oatey type
>> flashing dries and cracks
>> eventually.
>> Thanks for your insights..
>> Rich
>>
>
>
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20121126/3e45c545/attachment-0003.html>
More information about the RE-wrenches
mailing list