<div class="moz-cite-prefix"><font size="+1">JASON:<br>
<br>
I talked to Steve Capozzi of SolaDeck and he sent me additional
info about the circuit breakers:<br>
</font>
<blockquote><font size="+1"><u>Manufacturer</u>: ABB<br>
<br>
<u>Terminal Temp Rating</u>: 75C / 167F<br>
<br>
<u>Reference Temperature</u>: 20C / 68F<br>
<br>
<u>Ambient Temp Derating</u>: <br>
</font>
<blockquote><font size="+1">30C/86F = 18.7A<br>
40C/104F = 17.3A<br>
50C/122F = 15.8A<br>
60C/140F = 14.1A<br>
70C/158F = 12.2A<br>
</font></blockquote>
</blockquote>
<font size="+1"> My concern is that we may be attempting to use an
interior rated AC breaker in a roof-deck-mounted NEMA3-R
enclosure. <br>
<br>
In an Enphase application, with the maximum of 17 inverters per
AC Source Circuit, the continuous current will be 0.9A x 17 x
1.25 = 19.1A. This exceeds the 30C/86F trip current of 18.7A. <br>
<br>
The interior temperature of the SolaDeck could very likely
approach the 60C/140F trip current of 14.1A. <br>
<br>
It seems to me that "nuisance trips" could be a high probability
event. <br>
<br>
Does anyone have any field experience using this Soladeck option
for a AC Source Circuit Combiner Box (SCCB)?<br>
<br>
Another issue, at least in some jurisdictions, is the
requirement for a roof-top AC Disconnect. <br>
<br>
The SolaDeck, when used as an AC SCCB, may not meet the NEC
Article 100 requirements in some jurisdictions for "readily
accessible" because a tool is required to open it.<br>
<br>
<font color="#000000"> </font> <font color="#000000"> </font>
<font color="#000000"> </font> <font color="#000000"> </font>
<font color="#000000"> </font> </font>
<p class="" style="margin-bottom:0.0001pt;line-height:normal"><font
size="+1" color="#000000"><span>Regards<span>,</span><br>
<br>
<br>
Gary Willett, PE<br>
Icarus Engineering LLC</span></font></p>
<font size="+1"> <font color="#000000"> </font> <font
color="#000000"><span>Icarus Solar Services LLC</span></font></font>
<div class="moz-signature">
<meta http-equiv="Content-Type" content="text/html;
charset=ISO-8859-1">
<meta name="ProgId" content="Word.Document">
<meta name="Generator" content="Microsoft Word 12">
<meta name="Originator" content="Microsoft Word 12">
<link rel="File-List" href="GFW%20Signature_files/filelist.xml">
<!--[if gte mso 9]><xml>
<o:DocumentProperties>
<o:Author>Icarus</o:Author>
<o:LastAuthor>Gary Willett</o:LastAuthor>
<o:Revision>7</o:Revision>
<o:TotalTime>10</o:TotalTime>
<o:Created>2010-07-05T22:08:00Z</o:Created>
<o:LastSaved>2011-08-06T01:33:00Z</o:LastSaved>
<o:Pages>1</o:Pages>
<o:Words>37</o:Words>
<o:Characters>276</o:Characters>
<o:Lines>2</o:Lines>
<o:Paragraphs>1</o:Paragraphs>
<o:CharactersWithSpaces>312</o:CharactersWithSpaces>
<o:Version>12.00</o:Version>
</o:DocumentProperties>
</xml><![endif]-->
<link rel="themeData"
href="GFW%20Signature_files/themedata.thmx">
<link rel="colorSchemeMapping"
href="GFW%20Signature_files/colorschememapping.xml">
<!--[if gte mso 9]><xml>
<w:WordDocument>
<w:Zoom>BestFit</w:Zoom>
<w:SpellingState>Clean</w:SpellingState>
<w:GrammarState>Clean</w:GrammarState>
<w:TrackMoves/>
<w:TrackFormatting/>
<w:PunctuationKerning/>
<w:ValidateAgainstSchemas/>
<w:SaveIfXMLInvalid>false</w:SaveIfXMLInvalid>
<w:IgnoreMixedContent>false</w:IgnoreMixedContent>
<w:AlwaysShowPlaceholderText>false</w:AlwaysShowPlaceholderText>
<w:DoNotPromoteQF/>
<w:LidThemeOther>EN-US</w:LidThemeOther>
<w:LidThemeAsian>X-NONE</w:LidThemeAsian>
<w:LidThemeComplexScript>X-NONE</w:LidThemeComplexScript>
<w:Compatibility>
<w:BreakWrappedTables/>
<w:SnapToGridInCell/>
<w:WrapTextWithPunct/>
<w:UseAsianBreakRules/>
<w:DontGrowAutofit/>
<w:SplitPgBreakAndParaMark/>
<w:DontVertAlignCellWithSp/>
<w:DontBreakConstrainedForcedTables/>
<w:DontVertAlignInTxbx/>
<w:Word11KerningPairs/>
<w:CachedColBalance/>
</w:Compatibility>
<w:BrowserLevel>MicrosoftInternetExplorer4</w:BrowserLevel>
<m:mathPr>
<m:mathFont m:val="Cambria Math"/>
<m:brkBin m:val="before"/>
<m:brkBinSub m:val="--"/>
<m:smallFrac m:val="off"/>
<m:dispDef/>
<m:lMargin m:val="0"/>
<m:rMargin m:val="0"/>
<m:defJc m:val="centerGroup"/>
<m:wrapIndent m:val="1440"/>
<m:intLim m:val="subSup"/>
<m:naryLim m:val="undOvr"/>
</m:mathPr></w:WordDocument>
</xml><![endif]--><!--[if gte mso 9]><xml>
<w:LatentStyles DefLockedState="false" DefUnhideWhenUsed="true"
DefSemiHidden="true" DefQFormat="false" DefPriority="99"
LatentStyleCount="267">
<w:LsdException Locked="false" Priority="0" SemiHidden="false"
UnhideWhenUsed="false" QFormat="true" Name="Normal"/>
<w:LsdException Locked="false" Priority="9" SemiHidden="false"
UnhideWhenUsed="false" QFormat="true" Name="heading 1"/>
<w:LsdException Locked="false" Priority="9" QFormat="true" Name="heading 2"/>
<w:LsdException Locked="false" Priority="9" QFormat="true" Name="heading 3"/>
<w:LsdException Locked="false" Priority="9" QFormat="true" Name="heading 4"/>
<w:LsdException Locked="false" Priority="9" QFormat="true" Name="heading 5"/>
<w:LsdException Locked="false" Priority="9" QFormat="true" Name="heading 6"/>
<w:LsdException Locked="false" Priority="9" QFormat="true" Name="heading 7"/>
<w:LsdException Locked="false" Priority="9" QFormat="true" Name="heading 8"/>
<w:LsdException Locked="false" Priority="9" QFormat="true" Name="heading 9"/>
<w:LsdException Locked="false" Priority="39" Name="toc 1"/>
<w:LsdException Locked="false" Priority="39" Name="toc 2"/>
<w:LsdException Locked="false" Priority="39" Name="toc 3"/>
<w:LsdException Locked="false" Priority="39" Name="toc 4"/>
<w:LsdException Locked="false" Priority="39" Name="toc 5"/>
<w:LsdException Locked="false" Priority="39" Name="toc 6"/>
<w:LsdException Locked="false" Priority="39" Name="toc 7"/>
<w:LsdException Locked="false" Priority="39" Name="toc 8"/>
<w:LsdException Locked="false" Priority="39" Name="toc 9"/>
<w:LsdException Locked="false" Priority="35" QFormat="true" Name="caption"/>
<w:LsdException Locked="false" Priority="10" SemiHidden="false"
UnhideWhenUsed="false" QFormat="true" Name="Title"/>
<w:LsdException Locked="false" Priority="1" Name="Default Paragraph Font"/>
<w:LsdException Locked="false" Priority="11" SemiHidden="false"
UnhideWhenUsed="false" QFormat="true" Name="Subtitle"/>
<w:LsdException Locked="false" Priority="22" SemiHidden="false"
UnhideWhenUsed="false" QFormat="true" Name="Strong"/>
<w:LsdException Locked="false" Priority="20" SemiHidden="false"
UnhideWhenUsed="false" QFormat="true" Name="Emphasis"/>
<w:LsdException Locked="false" Priority="59" SemiHidden="false"
UnhideWhenUsed="false" Name="Table Grid"/>
<w:LsdException Locked="false" UnhideWhenUsed="false" Name="Placeholder Text"/>
<w:LsdException Locked="false" Priority="1" SemiHidden="false"
UnhideWhenUsed="false" QFormat="true" Name="No Spacing"/>
<w:LsdException Locked="false" Priority="60" SemiHidden="false"
UnhideWhenUsed="false" Name="Light Shading"/>
<w:LsdException Locked="false" Priority="61" SemiHidden="false"
UnhideWhenUsed="false" Name="Light List"/>
<w:LsdException Locked="false" Priority="62" SemiHidden="false"
UnhideWhenUsed="false" Name="Light Grid"/>
<w:LsdException Locked="false" Priority="63" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Shading 1"/>
<w:LsdException Locked="false" Priority="64" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Shading 2"/>
<w:LsdException Locked="false" Priority="65" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium List 1"/>
<w:LsdException Locked="false" Priority="66" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium List 2"/>
<w:LsdException Locked="false" Priority="67" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 1"/>
<w:LsdException Locked="false" Priority="68" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 2"/>
<w:LsdException Locked="false" Priority="69" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 3"/>
<w:LsdException Locked="false" Priority="70" SemiHidden="false"
UnhideWhenUsed="false" Name="Dark List"/>
<w:LsdException Locked="false" Priority="71" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful Shading"/>
<w:LsdException Locked="false" Priority="72" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful List"/>
<w:LsdException Locked="false" Priority="73" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful Grid"/>
<w:LsdException Locked="false" Priority="60" SemiHidden="false"
UnhideWhenUsed="false" Name="Light Shading Accent 1"/>
<w:LsdException Locked="false" Priority="61" SemiHidden="false"
UnhideWhenUsed="false" Name="Light List Accent 1"/>
<w:LsdException Locked="false" Priority="62" SemiHidden="false"
UnhideWhenUsed="false" Name="Light Grid Accent 1"/>
<w:LsdException Locked="false" Priority="63" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Shading 1 Accent 1"/>
<w:LsdException Locked="false" Priority="64" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Shading 2 Accent 1"/>
<w:LsdException Locked="false" Priority="65" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium List 1 Accent 1"/>
<w:LsdException Locked="false" UnhideWhenUsed="false" Name="Revision"/>
<w:LsdException Locked="false" Priority="34" SemiHidden="false"
UnhideWhenUsed="false" QFormat="true" Name="List Paragraph"/>
<w:LsdException Locked="false" Priority="29" SemiHidden="false"
UnhideWhenUsed="false" QFormat="true" Name="Quote"/>
<w:LsdException Locked="false" Priority="30" SemiHidden="false"
UnhideWhenUsed="false" QFormat="true" Name="Intense Quote"/>
<w:LsdException Locked="false" Priority="66" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium List 2 Accent 1"/>
<w:LsdException Locked="false" Priority="67" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 1 Accent 1"/>
<w:LsdException Locked="false" Priority="68" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 2 Accent 1"/>
<w:LsdException Locked="false" Priority="69" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 3 Accent 1"/>
<w:LsdException Locked="false" Priority="70" SemiHidden="false"
UnhideWhenUsed="false" Name="Dark List Accent 1"/>
<w:LsdException Locked="false" Priority="71" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful Shading Accent 1"/>
<w:LsdException Locked="false" Priority="72" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful List Accent 1"/>
<w:LsdException Locked="false" Priority="73" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful Grid Accent 1"/>
<w:LsdException Locked="false" Priority="60" SemiHidden="false"
UnhideWhenUsed="false" Name="Light Shading Accent 2"/>
<w:LsdException Locked="false" Priority="61" SemiHidden="false"
UnhideWhenUsed="false" Name="Light List Accent 2"/>
<w:LsdException Locked="false" Priority="62" SemiHidden="false"
UnhideWhenUsed="false" Name="Light Grid Accent 2"/>
<w:LsdException Locked="false" Priority="63" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Shading 1 Accent 2"/>
<w:LsdException Locked="false" Priority="64" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Shading 2 Accent 2"/>
<w:LsdException Locked="false" Priority="65" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium List 1 Accent 2"/>
<w:LsdException Locked="false" Priority="66" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium List 2 Accent 2"/>
<w:LsdException Locked="false" Priority="67" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 1 Accent 2"/>
<w:LsdException Locked="false" Priority="68" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 2 Accent 2"/>
<w:LsdException Locked="false" Priority="69" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 3 Accent 2"/>
<w:LsdException Locked="false" Priority="70" SemiHidden="false"
UnhideWhenUsed="false" Name="Dark List Accent 2"/>
<w:LsdException Locked="false" Priority="71" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful Shading Accent 2"/>
<w:LsdException Locked="false" Priority="72" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful List Accent 2"/>
<w:LsdException Locked="false" Priority="73" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful Grid Accent 2"/>
<w:LsdException Locked="false" Priority="60" SemiHidden="false"
UnhideWhenUsed="false" Name="Light Shading Accent 3"/>
<w:LsdException Locked="false" Priority="61" SemiHidden="false"
UnhideWhenUsed="false" Name="Light List Accent 3"/>
<w:LsdException Locked="false" Priority="62" SemiHidden="false"
UnhideWhenUsed="false" Name="Light Grid Accent 3"/>
<w:LsdException Locked="false" Priority="63" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Shading 1 Accent 3"/>
<w:LsdException Locked="false" Priority="64" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Shading 2 Accent 3"/>
<w:LsdException Locked="false" Priority="65" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium List 1 Accent 3"/>
<w:LsdException Locked="false" Priority="66" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium List 2 Accent 3"/>
<w:LsdException Locked="false" Priority="67" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 1 Accent 3"/>
<w:LsdException Locked="false" Priority="68" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 2 Accent 3"/>
<w:LsdException Locked="false" Priority="69" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 3 Accent 3"/>
<w:LsdException Locked="false" Priority="70" SemiHidden="false"
UnhideWhenUsed="false" Name="Dark List Accent 3"/>
<w:LsdException Locked="false" Priority="71" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful Shading Accent 3"/>
<w:LsdException Locked="false" Priority="72" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful List Accent 3"/>
<w:LsdException Locked="false" Priority="73" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful Grid Accent 3"/>
<w:LsdException Locked="false" Priority="60" SemiHidden="false"
UnhideWhenUsed="false" Name="Light Shading Accent 4"/>
<w:LsdException Locked="false" Priority="61" SemiHidden="false"
UnhideWhenUsed="false" Name="Light List Accent 4"/>
<w:LsdException Locked="false" Priority="62" SemiHidden="false"
UnhideWhenUsed="false" Name="Light Grid Accent 4"/>
<w:LsdException Locked="false" Priority="63" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Shading 1 Accent 4"/>
<w:LsdException Locked="false" Priority="64" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Shading 2 Accent 4"/>
<w:LsdException Locked="false" Priority="65" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium List 1 Accent 4"/>
<w:LsdException Locked="false" Priority="66" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium List 2 Accent 4"/>
<w:LsdException Locked="false" Priority="67" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 1 Accent 4"/>
<w:LsdException Locked="false" Priority="68" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 2 Accent 4"/>
<w:LsdException Locked="false" Priority="69" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 3 Accent 4"/>
<w:LsdException Locked="false" Priority="70" SemiHidden="false"
UnhideWhenUsed="false" Name="Dark List Accent 4"/>
<w:LsdException Locked="false" Priority="71" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful Shading Accent 4"/>
<w:LsdException Locked="false" Priority="72" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful List Accent 4"/>
<w:LsdException Locked="false" Priority="73" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful Grid Accent 4"/>
<w:LsdException Locked="false" Priority="60" SemiHidden="false"
UnhideWhenUsed="false" Name="Light Shading Accent 5"/>
<w:LsdException Locked="false" Priority="61" SemiHidden="false"
UnhideWhenUsed="false" Name="Light List Accent 5"/>
<w:LsdException Locked="false" Priority="62" SemiHidden="false"
UnhideWhenUsed="false" Name="Light Grid Accent 5"/>
<w:LsdException Locked="false" Priority="63" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Shading 1 Accent 5"/>
<w:LsdException Locked="false" Priority="64" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Shading 2 Accent 5"/>
<w:LsdException Locked="false" Priority="65" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium List 1 Accent 5"/>
<w:LsdException Locked="false" Priority="66" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium List 2 Accent 5"/>
<w:LsdException Locked="false" Priority="67" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 1 Accent 5"/>
<w:LsdException Locked="false" Priority="68" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 2 Accent 5"/>
<w:LsdException Locked="false" Priority="69" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 3 Accent 5"/>
<w:LsdException Locked="false" Priority="70" SemiHidden="false"
UnhideWhenUsed="false" Name="Dark List Accent 5"/>
<w:LsdException Locked="false" Priority="71" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful Shading Accent 5"/>
<w:LsdException Locked="false" Priority="72" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful List Accent 5"/>
<w:LsdException Locked="false" Priority="73" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful Grid Accent 5"/>
<w:LsdException Locked="false" Priority="60" SemiHidden="false"
UnhideWhenUsed="false" Name="Light Shading Accent 6"/>
<w:LsdException Locked="false" Priority="61" SemiHidden="false"
UnhideWhenUsed="false" Name="Light List Accent 6"/>
<w:LsdException Locked="false" Priority="62" SemiHidden="false"
UnhideWhenUsed="false" Name="Light Grid Accent 6"/>
<w:LsdException Locked="false" Priority="63" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Shading 1 Accent 6"/>
<w:LsdException Locked="false" Priority="64" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Shading 2 Accent 6"/>
<w:LsdException Locked="false" Priority="65" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium List 1 Accent 6"/>
<w:LsdException Locked="false" Priority="66" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium List 2 Accent 6"/>
<w:LsdException Locked="false" Priority="67" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 1 Accent 6"/>
<w:LsdException Locked="false" Priority="68" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 2 Accent 6"/>
<w:LsdException Locked="false" Priority="69" SemiHidden="false"
UnhideWhenUsed="false" Name="Medium Grid 3 Accent 6"/>
<w:LsdException Locked="false" Priority="70" SemiHidden="false"
UnhideWhenUsed="false" Name="Dark List Accent 6"/>
<w:LsdException Locked="false" Priority="71" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful Shading Accent 6"/>
<w:LsdException Locked="false" Priority="72" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful List Accent 6"/>
<w:LsdException Locked="false" Priority="73" SemiHidden="false"
UnhideWhenUsed="false" Name="Colorful Grid Accent 6"/>
<w:LsdException Locked="false" Priority="19" SemiHidden="false"
UnhideWhenUsed="false" QFormat="true" Name="Subtle Emphasis"/>
<w:LsdException Locked="false" Priority="21" SemiHidden="false"
UnhideWhenUsed="false" QFormat="true" Name="Intense Emphasis"/>
<w:LsdException Locked="false" Priority="31" SemiHidden="false"
UnhideWhenUsed="false" QFormat="true" Name="Subtle Reference"/>
<w:LsdException Locked="false" Priority="32" SemiHidden="false"
UnhideWhenUsed="false" QFormat="true" Name="Intense Reference"/>
<w:LsdException Locked="false" Priority="33" SemiHidden="false"
UnhideWhenUsed="false" QFormat="true" Name="Book Title"/>
<w:LsdException Locked="false" Priority="37" Name="Bibliography"/>
<w:LsdException Locked="false" Priority="39" QFormat="true" Name="TOC Heading"/>
</w:LatentStyles>
</xml><![endif]-->
<style>
<!--
/* Font Definitions */
@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;
mso-font-charset:1;
mso-generic-font-family:roman;
mso-font-format:other;
mso-font-pitch:variable;
mso-font-signature:0 0 0 0 0 0;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;
mso-font-charset:0;
mso-generic-font-family:swiss;
mso-font-pitch:variable;
mso-font-signature:-520092929 1073786111 9 0 415 0;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{mso-style-unhide:no;
mso-style-qformat:yes;
mso-style-parent:"";
margin-top:0in;
margin-right:0in;
margin-bottom:10.0pt;
margin-left:0in;
line-height:115%;
mso-pagination:widow-orphan;
font-size:11.0pt;
font-family:"Calibri","sans-serif";
mso-ascii-font-family:Calibri;
mso-ascii-theme-font:minor-latin;
mso-fareast-font-family:Calibri;
mso-fareast-theme-font:minor-latin;
mso-hansi-font-family:Calibri;
mso-hansi-theme-font:minor-latin;
mso-bidi-font-family:"Times New Roman";
mso-bidi-theme-font:minor-bidi;}
a:link, span.MsoHyperlink
{mso-style-noshow:yes;
mso-style-priority:99;
color:blue;
text-decoration:underline;
text-underline:single;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-noshow:yes;
mso-style-priority:99;
color:purple;
mso-themecolor:followedhyperlink;
text-decoration:underline;
text-underline:single;}
span.GramE
{mso-style-name:"";
mso-gram-e:yes;}
.MsoChpDefault
{mso-style-type:export-only;
mso-default-props:yes;
font-size:10.0pt;
mso-ansi-font-size:10.0pt;
mso-bidi-font-size:10.0pt;
mso-ascii-font-family:Calibri;
mso-ascii-theme-font:minor-latin;
mso-fareast-font-family:Calibri;
mso-fareast-theme-font:minor-latin;
mso-hansi-font-family:Calibri;
mso-hansi-theme-font:minor-latin;
mso-bidi-font-family:"Times New Roman";
mso-bidi-theme-font:minor-bidi;}
@page WordSection1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;
mso-header-margin:.5in;
mso-footer-margin:.5in;
mso-paper-source:0;}
div.WordSection1
{page:WordSection1;}
-->
</style><!--[if gte mso 10]>
<style>
/* Style Definitions */
table.MsoNormalTable
{mso-style-name:"Table Normal";
mso-tstyle-rowband-size:0;
mso-tstyle-colband-size:0;
mso-style-noshow:yes;
mso-style-priority:99;
mso-style-qformat:yes;
mso-style-parent:"";
mso-padding-alt:0in 5.4pt 0in 5.4pt;
mso-para-margin:0in;
mso-para-margin-bottom:.0001pt;
mso-pagination:widow-orphan;
font-size:10.0pt;
font-family:"Calibri","sans-serif";
mso-ascii-font-family:Calibri;
mso-ascii-theme-font:minor-latin;
mso-hansi-font-family:Calibri;
mso-hansi-theme-font:minor-latin;
mso-bidi-font-family:"Times New Roman";
mso-bidi-theme-font:minor-bidi;}
</style>
<![endif]--><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026"/>
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1"/>
</o:shapelayout></xml><![endif]-->
<div class="WordSection1"><br>
<span
style="mso-ascii-font-family:Calibri;mso-hansi-font-family:Calibri;
mso-bidi-font-family:Calibri"><o:p></o:p></span>
</div>
</div>
On 11/26/2012 2:21 PM, Jason Szumlanski wrote:<br>
</div>
<blockquote
cite="mid:CAJJtG3ryOtMkbiz9HzxcuLd0H0H6ViUBx8fW+sxCMTie9zQXTQ@mail.gmail.com"
type="cite">I did get some pictures and info from Soladeck. Here
are some links:
<div><br>
</div>
<div>Pics:</div>
<div>
<div><a moz-do-not-send="true"
href="https://docs.google.com/open?id=1BpiL-1SdSNNsj4wPMQrFCLHH7JT2dek_KftSJl06QLqc0yhJ_1t5oij0aEA6">https://docs.google.com/open?id=1BpiL-1SdSNNsj4wPMQrFCLHH7JT2dek_KftSJl06QLqc0yhJ_1t5oij0aEA6</a></div>
<div><a moz-do-not-send="true"
href="https://docs.google.com/open?id=1cVuhZGeQNHL1IvGvNBa7v93oZyGBvjxCv5yq4AmoyJeDAITxvgMqgECR2yTv">https://docs.google.com/open?id=1cVuhZGeQNHL1IvGvNBa7v93oZyGBvjxCv5yq4AmoyJeDAITxvgMqgECR2yTv</a></div>
<div><a moz-do-not-send="true"
href="https://docs.google.com/open?id=1umslTplnFyZG1eNCZE-MMi_OqrSeirFCPRBl9mFNZJ2gQkBjM5LEXnaPKy2l">https://docs.google.com/open?id=1umslTplnFyZG1eNCZE-MMi_OqrSeirFCPRBl9mFNZJ2gQkBjM5LEXnaPKy2l</a></div>
<div>Specs:</div>
<div>
<div><a moz-do-not-send="true"
href="https://docs.google.com/open?id=13KLAuxUHOR9al7-36reDSJJ7IMnqV3ANPnJILPnrj2xcAi0ksRj67ifKIe7R">https://docs.google.com/open?id=13KLAuxUHOR9al7-36reDSJJ7IMnqV3ANPnJILPnrj2xcAi0ksRj67ifKIe7R</a></div>
<div><a moz-do-not-send="true"
href="https://docs.google.com/open?id=1kvPFcDc1vruS3W_aONlXyIHm1T8-qi4vTpTwGGJ7H0eIwuZ-5e6zrM1CcND5">https://docs.google.com/open?id=1kvPFcDc1vruS3W_aONlXyIHm1T8-qi4vTpTwGGJ7H0eIwuZ-5e6zrM1CcND5</a></div>
<div><a moz-do-not-send="true"
href="https://docs.google.com/open?id=1lM8FtYl9HiYohru32UA_Gb1tXZKZ5iw-8tnSu1Un6g4vcklLL-DK1qLPMdsB">https://docs.google.com/open?id=1lM8FtYl9HiYohru32UA_Gb1tXZKZ5iw-8tnSu1Un6g4vcklLL-DK1qLPMdsB</a></div>
</div>
<div><br>
</div>
<div>I was told Soligent can source the combiners for you (and
me).<br>
<br>
<div>
<div
style="font-size:13px;font-family:Verdana,Arial,Helvetica,sans-serif">
<div style="margin:0px 0px 8px">
<p style="margin:0px"><span
style="color:rgb(128,128,128)"><strong>Jason
Szumlanski</strong><em> </em></span></p>
<p style="margin:0px"><span
style="color:rgb(128,128,128)"><em>Fafco Solar</em></span><a
moz-do-not-send="true"
href="http://www.wisestamp.com/apps/wordpress?utm_source=extension&utm_medium=email&utm_term=wordpress&utm_campaign=apps"
target="_blank"
style="font-family:arial,sans-serif;font-size:80%;color:gray;text-decoration:initial"> </a><span
style="color:gray;font-family:arial,sans-serif;font-size:80%"> </span></p>
</div>
</div>
</div>
<div class="gmail_extra"><br>
<div class="gmail_quote">On Mon, Nov 26, 2012 at 1:50 PM,
Jason Szumlanski <span dir="ltr"><<a
moz-do-not-send="true"
href="mailto:jason@fafcosolar.com" target="_blank">jason@fafcosolar.com</a>></span>
wrote:<br>
<blockquote class="gmail_quote" style="margin:0px 0px 0px
0.8ex;border-left-width:1px;border-left-color:rgb(204,204,204);border-left-style:solid;padding-left:1ex">I
just called Soladeck and they are sending me some more
info on availability. I'll pass it along when I get it.
I didn't realize they made an AC roof mounted string
combiner solution. That's a huge help for 2 or 3 string
Enphase installations (they make both combiners).
<div>
<br>
</div>
<div>While on the subject, we recently started using the
Enphase cable couple with Type TC-ER cable to extend
cabling to junction boxes when necessary... No more
wasting trunk cable connectors! I suppose Type TC-ER
could be used all the way to the main distribution
panel, thereby eliminating junctions on the roof, but
I haven't looked into the cost/benefit of that idea.<br>
<div><br>
</div>
<div>
<div>
<div
style="font-size:13px;font-family:Verdana,Arial,Helvetica,sans-serif">
<div style="margin:0px 0px 8px">
<p style="margin:0px"><span
style="color:rgb(128,128,128)"><strong>Jason
Szumlanski</strong></span></p>
<p style="margin:0px"><span
style="color:rgb(128,128,128)"><em>Fafco
Solar</em></span><br>
<br>
</p>
</div>
</div>
</div>
</div>
</div>
<div>
<div>
<div class="gmail_extra"><br>
<br>
<div class="gmail_quote">On Mon, Nov 26, 2012 at
1:26 PM, Gary Willett <span dir="ltr"><<a
moz-do-not-send="true"
href="mailto:gary@icarussolarservices.com"
target="_blank">gary@icarussolarservices.com</a>></span>
wrote:<br>
<blockquote class="gmail_quote"
style="margin:0px 0px 0px
0.8ex;border-left-width:1px;border-left-color:rgb(204,204,204);border-left-style:solid;padding-left:1ex">
<div text="#000000" bgcolor="#FFFFFF">
<div><font size="+1">NICK:<br>
<br>
I could not find the AC model numbers
you provided on the SolaDeck web si<font
size="+1">te. Do you know <font
size="+1">the manufacturer, and </font>the
vol<font size="+1">tage and
temperature ratings, for the 2-pole
20A AC breakers?</font></font><br>
<br>
</font>
<div><font color="#000000"> </font> <font
color="#000000"> </font> <font
color="#000000"> </font> <font
color="#000000"> </font>
<div><font color="#000000"> </font>
<p class=""
style="margin-bottom:0.0001pt;line-height:normal"><font
color="#000000"><span>Regards<span>,</span><br>
<br>
<br>
Gary Willett, PE<br>
Icarus Engineering LLC</span></font></p>
<font color="#000000"> </font>
<p class=""
style="margin-bottom:0.0001pt;line-height:normal"><font
color="#000000"><span>Icarus Solar
Services LLC<br>
</span><br>
</font><br>
</p>
</div>
</div>
<div>
<div> On 11/26/2012 11:54 AM, Nick
Soleil wrote:<br>
</div>
</div>
</div>
<div>
<div>
<blockquote type="cite">Hi wrenches;<br>
<br>
SolaDeck Models 0760-41AD and
0766-41AD are rated for up to 60A at
240Vac.<br>
<br>
It can be ordered with DIN rail
mounted AC breakers and a combiner
kit. The 2 - 20A circuit combiner kit
is part 0760K2AC.<br>
<br>
I'd recommend checking with a
distributor or on SolaDeck's website
for the most current information.<br>
<br>
Nick Soleil,<br>
Enphase Energy<br>
<div class="gmail_extra"><br>
<br>
<div class="gmail_quote">On Sun, Nov
25, 2012 at 7:44 AM, Kent
Osterberg <span dir="ltr"><<a
moz-do-not-send="true"
href="mailto:kent@coveoregon.com"
target="_blank">kent@coveoregon.com</a>></span>
wrote:<br>
<blockquote class="gmail_quote"
style="margin:0px 0px 0px
0.8ex;border-left-width:1px;border-left-color:rgb(204,204,204);border-left-style:solid;padding-left:1ex">My
understanding has been that the
Soladeck has only been listed
for DC wiring. Perhaps they have
a manufacturer rep on
RE-wrenches that can clarify.<span><font
color="#888888"><br>
<br>
Kent Osterberg<br>
Blue Mountain Solar, Inc.<br>
<a moz-do-not-send="true"
href="http://www.bluemountainsolar.com"
target="_blank">www.bluemountainsolar.com</a></font></span>
<div>
<div><br>
<br>
<br>
On 11/25/2012 6:20 AM, Dave
Palumbo wrote:<br>
<blockquote
class="gmail_quote"
style="margin:0px 0px 0px
0.8ex;border-left-width:1px;border-left-color:rgb(204,204,204);border-left-style:solid;padding-left:1ex">
Rich,<br>
<br>
We have been using
SolaDeck PV roof mount
enclosure. NEMA 3R with a
flashed<br>
penetration. Can use for
combining, or simply as a
pass through box.<br>
<br>
Dave<br>
<br>
David Palumbo<br>
Independent Power LLC<br>
462 Solar Way Drive<br>
Hyde Park, VT 05655<br>
<a moz-do-not-send="true"
href="http://www.independentpowerllc.com" target="_blank">www.independentpowerllc.com</a><br>
NABCEP Certified PV
Installer<br>
Vermont Solar Partner<br>
25 Years Experience, <a
moz-do-not-send="true"
href="tel:%28802%29%20888-7194"
value="+18028887194"
target="_blank">(802)
888-7194</a><br>
<br>
<br>
<br>
<br>
-----Original Message-----<br>
From: <a
moz-do-not-send="true"
href="mailto:re-wrenches-bounces@lists.re-wrenches.org"
target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a><br>
[mailto:<a
moz-do-not-send="true"
href="mailto:re-wrenches-bounces@lists.re-wrenches.org"
target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>]
On Behalf Of Rich Nicol<br>
Sent: Sunday, November 25,
2012 8:11 AM<br>
To: 'RE-wrenches'<br>
Subject: [RE-wrenches]
Best practices for conduit
penetration on roof<br>
<br>
Wrenches,<br>
We typically run conduit
for roof mounts over the
edge of the roof to the<br>
eaves, rather than
penetrate the roof
whenever possible. An
upcoming<br>
installation on an freshly
asphalt shingled roof
requires that we penetrate<br>
the roof for the conduit
run (Enphase). I'm
wondering if there are any<br>
suggestions for preferred
flashing products and best
known practices. It's<br>
always seemed to me that
the typical Oatey type
flashing dries and cracks<br>
eventually.<br>
Thanks for your insights..<br>
Rich<br>
<br>
</blockquote>
</div>
</div>
</blockquote>
</div>
</div>
</blockquote>
</div>
</div>
</div>
</blockquote>
</div>
</div>
</div>
</div>
</blockquote>
</div>
<br>
</div>
</div>
<br>
<br>
<br>
<br>
<br>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
List sponsored by Home Power magazine
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
</pre>
</blockquote>
<br>
</body>
</html>