FWIW: In the 2011 Code, Section 690.31(D) is changed to include the following:

"Where dc photovoltaic source or output circuits…are run inside a building or restructure, they shall be contained in metal raceways,Type MC metal-clad cable that complies with 250.118(10), or metal enclosures…"


On Nov 3, 2012, at 10:41 AM, Nick Vida wrote:

> Hello wrenches,
> 
> wondering if any of you are running into inspectors wanting EMT in the attics, or allowing flex only if there is a fusible disconnect on the roof. We have heard this a few time lately and havent yet seen a code reference, (except 690.31e saying metal raceways are fine- not specifying EMT only). I am wondering if this is a new wave of inspectors wanting the future now as informed by an expert seminar, or if there is something I am not aware of. Any comments are very appreciated.
> 
> Thank you,
> 
> Nick Vida