Jeff Wongstrom jeff.wongstrom at thirstylakesolar.com
Tue Oct 9 09:20:34 PDT 2012


Kent,

I just talked with Mike in the meter department.  The utility does indeed use Aclara TWACs AMR.  The meter reading signal can vary but is usually done at midnight or it could be set to every 8 hours, 1 hour, etc.  However, a time sync signal is sent every 15 minutes.  This correlates with the problem inverter going into state 104's at various times after connecting to the grid observed from 1-11 minutes.  Unfortunately I was informed that the time sync signal can not be changed.

Mike told me that there are two or three other Fronius inverters on their system without problems, he did not know if they are IG or IG+.

Jeff



Jeff Wongstrom
NABCEP Certified
406.291.3416
thirstylakesolar.com





On Oct 8, 2012, at 7:38 PM, Kent Osterberg wrote:

> Jeff,
> 
> Is there any chance the utility has recently implemented a remote meter reading system? The Aclara TWACs remote meter reading system communicates by putting a pulse on the line that is very near the zero crossing of the voltage waveform. Unfortunately the zero crossing is easily and often used as a reference point for frequency measurements. Devices that watch the zero crossings are often confused by the TWACS signal. The signal isn't there constantly -- only when the local kWr meter has been asked to send data.
> Kent Osterberg
> Blue Mountain Solar, Inc.
> www.bluemountainsolar.com
> t: 541-568-4882
> On 10/8/2012 9:34 AM, Jeff Wongstrom wrote:
>> Hello wrenches,
>> 
>> We have a Fronius IG3000 that chronically and frequently cycles into and out of a state 104(grid frequency not within admissible range).   The utility has monitored the supply and claims to have found no frequency or supply issues.   Fronius sent a replacement inverter but the error persists. The tie in point was moved from the critical loads sub panel to the main distribution panel.  The state 104 persists with ALL other breakers open.  A Fluke DMM min/max function captures no frequency readings outside of the inverter frequency window-same with voltage readings.   
>> 
>> Any suggestions or recommendations?
>> 
>> Thanks,
>> 
>> Jeff
>> 
>> <Mail Attachment.jpeg>
>> Jeff Wongstrom
>> NABCEP Certified
>> 406.291.3416
>> thirstylakesolar.com
>> 
>> 
>> 
>> 
>> 
>> 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20121009/4f4dba24/attachment-0003.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: LOGO.jpg
Type: image/jpeg
Size: 5311 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20121009/4f4dba24/attachment-0006.jpg>


More information about the RE-wrenches mailing list