Hello Jeff,

I am curious about the network of ground rods and #6 wire. Can you describe how the modules and mount are connected to this ground system? 
Are there any tight bends anywhere in the #6 wire? 
Are any of the poles or mounts connected to other poles/mounts before going to the ground system? 
Are any PV wires running between the poles before going to the combiner? 

As most wrenches know, lightning strikes can induce very high voltage on any nearby wire runs and that voltage is looking for a path to ground. Equipment is damaged when it contributes to that path. If the voltage was induced on the PV module frames or wire, an effective ground system will disperse it to ground. Key word here is effective. I have seen grounding systems where the installer made nice, neat and tight 90° bends in the ground wire. This is a huge mistake which can greatly diminish the effectiveness of the ground system. 

Larry Crutcher
Starlight Solar Power Systems



On Sep 7, 2012, at 8:40 AM, Jeff Irish wrote:

A customer of ours has recently suffered lightning damage to 31 out of 160 top of pole mounted modules.  This is the first time in 10 years that I’ve seen modules damaged by lightning.  Lots of inverter GF fuses and a few inverters, but never modules.  We’re trying to determine if it was caused by the lightning flash irradiating the modules or ground currents. 
 
The array consists of 16 DP&W top of pole mounts with 10 modules each, arranged in a square of 4 poles E-W and 4 rows N-S.  The poles are 13 feet center to center E-W and the N-S row spacing is about 50 feet.  The poles are 6 inch galvanized Technoposts, augured 5 – 7 feet into the firm ground, connected with a network of about 160 feet of bare #6 copper and at least 8 copper plated ground rods.  Altogether we have about 130 square feet of bare metal surface area connected and buried in the ground at and around the array.
 
The customer saw lightning strike just after dawn a few weeks ago a couple hundred feet to the southwest where it also destroyed two utility pole mount distribution transformers and ran along the utility wires 100 feet south of the array.  The inverters are 200 feet NW and suffered no damage.  The array and modules look totally fine, except some of the J-boxes are deformed from heat.  Opening the J-boxes shows varying levels of damage to one or more diodes, from discoloration to being broken and cracked open. 
 
The odd thing is the pattern of damage (we’ve tested all the modules individually for Voc and Isc).  Only modules in the south row of 4 poles are damaged, and the damage is concentrated on the modules closest to the ground; modules higher up in the air appear OK.  Also, damage is less frequent as you move east, away from the direction of the strike. 
 
If it was caused by ground currents, why would the current want to go up the poles, why only the southern row of poles, and why damage more modules closer to the ground and not those at the top?  Is it possible a flash near the ground irradiated the modules causing a current spike and the southern row shielded the other rows from most of the flash?  Anyone have experience with this?
 
 
Jeff Irish, PE
President
Hudson Solar
13 Hook Road
Rhinebeck, NY 12572
T.845.876.3767x110
F.845.876.3912
jeff at hudsonsolar.com
Solar Electric Systems
NYSERDA Eligible PV Installer
NABCEP Certified Solar PV Installer
NABCEP Certified PV Technical Sales
HudsonSolar.com
2011 NYSERDA Excellence in Quality Award | 2011 NYSEIA Award Winner | 2009 Best of the Hudson Valley | 2008 SunPower Dealer of the Year | EDC Business Excellence Award for Innovation
 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120907/f0b89847/attachment-0003.html>


More information about the RE-wrenches mailing list