I second using QO load centers.  You will want to put a fuse, like an 
FRN-R, between the battery and the load center, as the QO breakers 
don't have a high AIC rating. 12 V systems can be wired as easily as 
a regular AC system.


At 05:05 PM 8/9/2012, you wrote:
>Hello,
>
>I've been looking at a lot of hunting shacks, fish houses and other 
>12V loads setups and was wondering how people go about setting these 
>up? What are people using for load termination, fusing?
>
>I'd like to keep all disconnects and fusing in one "box".
>
>Jesse
>