[RE-wrenches] 12V loads
Drake
drake.chamberlin at redwoodalliance.org
Fri Aug 10 15:35:10 PDT 2012
I second using QO load centers. You will want to put a fuse, like an
FRN-R, between the battery and the load center, as the QO breakers
don't have a high AIC rating. 12 V systems can be wired as easily as
a regular AC system.
At 05:05 PM 8/9/2012, you wrote:
>Hello,
>
>I've been looking at a lot of hunting shacks, fish houses and other
>12V loads setups and was wondering how people go about setting these
>up? What are people using for load termination, fusing?
>
>I'd like to keep all disconnects and fusing in one "box".
>
>Jesse
>
>Sent from my iPhone
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
More information about the RE-wrenches
mailing list