[RE-wrenches] Small battery bank vs too large array

Drake drake.chamberlin at redwoodalliance.org
Thu Aug 2 13:06:04 PDT 2012


Hello Wrenches,

Thanks for your help with this question.

I've had a breakthrough on the design of this system.  I talked with 
Tom at Midnight Solar, and he explained that Concord batteries can be 
charged at C X 5 if necessary, i.e., 5 X AH capacity of the 
bank.  The batteries like a fast charge.  They are a bit spendy, but 
will simplify the overall system design.

 From the Manual:
"The charging current during the Bulk stage should be set as high as 
practical; higher current mean faster recharge time.  For repetitive 
deep cycling, chargers should have an output current of at least 0.2C 
(20 Amps for a 100 Ah battery).  If the output current is less than 
this value, the cycle life of the battery may be negatively 
affected.  Due to low impedance design, Sun Xtender batteries can 
tolerate in-rush current levels as high as 5C (500 A for a 100 Ah battery). "

It is imperative to keep the system voltage at the required set 
point.  The CC regulation will prevent the batteries from being 
harmed, as the voltage will rise quickly.

Drake