[RE-wrenches] PV harvest in grid-tied systems
William Miller
william at millersolar.com
Mon Apr 16 07:56:12 PDT 2012
Chris:
I would willingly clarify but I am confused about what you are confused
about. I think we are saying the same thing about off-grid systems: If
you don't consume power, battery voltage stays high and charge controllers
reduce energy harvest.
William Miller
At 06:57 AM 4/16/2012, you wrote:
>William,
>I must confess to being totally confused by your post.
>
>I am currently at my office writing to you using electricity from our
>off-grid solar system. We only have the solar power, no grid power.
>
>We get exactly as much power as I predicted we would, in fact a little
>more. But, there is an intrinsic issue with off-grid systems that many
>people miss. Unless you have a use for the power, it won't be "harvested".
>If you allow the inverter to charge the batteries from the grid, there
>will be nowhere for the PV power to go.
>
>To give you an example, our warehouse and office has 2,580 watts of PV on
>a 60 amp charge controller and a 3.5KW outback inverter, with 250Ah of
>VRLA batteries (4 x 12V).
>
>Each day, I read the amount of power the charge controller makes. It
>averages about 12KWh, depending on how much we used that day and the state
>of the batteries at the beginning of the day. We have found that the loads
>did not adequately exploit the power product capabilities of the system,
>so we moved our freezer from the house to the warehouse to use up some
>more power.
>
>As we are in the Caribbean, the insolation levels are pretty continuous,
>so it does make calculations easier.
>
>
>Chris
>
>
>
>On Mon, Apr 16, 2012 at 1:50 AM, William Miller
><<mailto:william at millersolar.com>william at millersolar.com> wrote:
>Friends:
>
>There has been recent discussion on this forum about PV production in
>grid-tied with battery systems. I have been faced with this same problem
>in a 3 XW system installed in 2009.
>
>The customer's power bill never went down. PV harvest was abysmal. The
>system would create great short circuit current but would not harvest into
>the batteries.
>
>It is starting to appear the XW firmware was at fault. The inverters
>would charge the batteries too high so the charge controllers would back
>off. Upgraded firmware seems to be helping, but the data set is still limited.
>
>Remember this: just because a PV system can produce does not mean it
>will. The charge controller knows only one thing: battery voltage. If
>it is high, production is curtailed.
>
>Off-grid production will also be reduced is consumption is curtailed.
>
>Charge controllers that can be set for grid-tied applications help, but
>only if the inverter(s) do not keep the battery voltage too high.
>
>William Miller
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120416/516b4613/attachment-0003.html>
More information about the RE-wrenches
mailing list