A few years back I made some year long measurements on an outback GVFX and a sunny boy for net energy to the grid I got only a few percentages not 10%  I think one of the problems is the battery selection, these new batteries from Outback seem to have very low self discharge so very little energy should be expended to keep them charged.  I am trying to close on a system where the distance from the solar array to the house is far, so I am planning to AC couple to a Radian to the grid, and I have been sucessful with AC coupleing on GVFXs and Outback assures me it will workas well with theRradian.  This install is very sensitive to LOL (loss of load) and has the generator ready to go, but for the short outages that he has it is a hassel.  (he has worn out one generator all ready, it was a construction grade genny)  
 
I am hoping if this system is a go to consider a Xantrex 600 volt charge controller, but it depends upon the customer
thanks for the patence 
Darryl
 

________________________________
 From: Drake <drake.chamberlin at redwoodalliance.org>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org> 
Sent: Friday, March 2, 2012 9:31 AM
Subject: Re: [RE-wrenches] Grid-Tied, PV by AC or DC
  

I think the AC coupled approach would be the best.  For the 10KW
system, a pair of Sunny Islands fed by Sunny Boys would make an efficient
system.  Since there is no generator, the system should be fairly
straight forward. 

At 02:06 AM 3/2/2012, you wrote:


i
think mark was asking more about ac coupling to get away from the
horrible inefficiencies of battery based, grid-tied inverters.
>
> 
>
>as an experiment, i have been thinking about ac coupling one (or more) of
my arrays on my outback system to gain 10% over having the gvfx do the
selling.
>
> 
>
>stc to ptc usually costs about 20%, then losing another 10% in the
inverter is a real performance hit. i advise customers about phantom
loads and conservation, when actually the battery based inverter is
itself the big lump under the carpet!
>
> 
>
>todd
>
> 
>
> 
>
> 
>
> 
>
> 
>
>On Thursday, March 1, 2012 7:07pm, "Maverick Brown [Maverick
Solar]" <maverick at mavericksolar.com> said:
>
>My two cents:
>"battery-based inverter w/ PV on the DC side via charge
controllers"
>Simply replace the GT inverter with a Xantrex 600V Charge Controller plus
the 48V Grid Interactive Inverter of your choice and added battery bank,
etc.
>Until the market is saturated with unneeded GT Inverters, you will be ok.
;-)
>Try your best to provide enough battery for at least 24 hours of outage
at 50% DOD. You may have add a Sub-Panel or Manual Transfer Switch.
>Thanks
>Maverick
>Maverick Brown
>BSEET, NABCEP Certified Solar PV Installer ® # 091209-26
>President & CEO
>Maverick Solar Enterprises, Inc.
>Billing:  PO BOX 1229, Dripping Springs, TX 78620
>Office:       512-919-4493
>Fax:          
512-607-6398
>Cell:         
512-460-9825
>Corporate:
http://www.mavericksolarenterprises.com/
>
>
>
>________________________________
> From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of toddcory at finestplanet.com
>Sent: Thursday, March 01, 2012 5:46 PM
>To: RE-wrenches
>Cc: 'RE-wrenches'
>Subject: Re: [RE-wrenches] Grid-Tied, PV by AC or DC
>
>excellent question mark... and one which has been on my mind as well,
being most of my work is bbgt.
>
> 
>
>todd
>
> 
>
> 
>
> 
>
>On Thursday, March 1, 2012 11:37am, "Mark Frye"
<markf at berkeleysolar.com> said:
>
>Folks,
>
>I have a residential grid-tied customer in a net metered utility with a
favorable TOU rate.
>
>They could use about 10 kW of PV to offset 100% of their usage.
>
>But, they also complain about regular power outages in their neigborhood.
They don't want a generator.
>
>With reliable AC coupling now available, do we yet know which is the more
advantagous architecture; grid-tied, battery-based inverter w/ PV on the
DC side via charge controllers, or grid-tied, battery-based inverter w/
PV AC coupled via grid-tied, utility-based inverter?
>
>Your thoughts? 
>
>Mark Frye 
>Berkeley Solar Electric Systems 
>303 Redbud Way 
>Nevada City,  CA 95959 
>(530) 401-8024 
>www.berkeleysolar.com 
>
>
>
>Sent from Finest Planet WebMail.
>
>
>
>Sent from Finest Planet WebMail.
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>
>List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org 
Drake
Chamberlin          
ATHENS ELECTRIC LLC
OH License
44810         
CO license 3773
NABCEP Certified PV
 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120303/0e26b85b/attachment-0003.html>


More information about the RE-wrenches mailing list