On 1/4/2012 3:01 PM, All Solar, Inc. wrote:
> Wrenches,
> Once again I am trying to size a grid tie w/battery system and I
> struggle a little with the efficiencies of them.
> With PV Watts (v.1), is changing the DC to AC derate an accurate
> method for getting the output?
> Thanks in advance!
> Jeremy
If you keep the batteries charged to a voltage just above their resting
voltage,
say, 52 volts for a 48V system, and the battery bank isn't too large,
(~225 A-hours,
maybe a bit more), about 90% PV to grid AC efficiency is in the ball park.
That's what we figured in the early days of GFX inverters at OB. That's
giving
5% for the electronics and 5% for keeping up the batteries.
Different and/or more accurate information may have come along since
that time.
boB
> All Solar Inc.
> Jeremy and Amy Rodriguez
> 1463 M St
> Penrose, CO 81240
> www.asolarelectric.com <http://www.asolarelectric.com>
> Phone 719-372-3808
> Fax 719-372-3804
> Email allsolar at scswifi.net <mailto:allsolar at scswifi.net>
> Email allsolar at live.com <mailto:allsolar at live.com>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options& settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules& etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20120104/fbe5c437/attachment-0003.html>
More information about the RE-wrenches
mailing list