[RE-wrenches] Convert Grid Tie SW4048 to Backup System; Add New Inverter, AC Coupled
Nathan Jones
solardude97 at yahoo.com
Tue Nov 22 09:27:19 PST 2011
David,
Thanks for the early posts re. your experimentation and to Allan for reposting them. I have used a single switch in an off/on mode for AC coupled regulation where flooded batteries are used. On the AGM setups, which are a better battery in my opinion for AC coupling, I use the Morningstar relay driver and resistive heating elements to bleed progressively more power from the GTI to mimic 3 stage charging. When float stage is achieved I use a switch with both time and voltage input capability to shut down the GTI completely. This setup seems to work as we haven't had battery issues come up yet and a couple of these systems have been through a couple of weeks of off grid operation due to ice storms wrecking the local grid.
I have followed this thread with interest and was glad for the repost and subsequent discussion.
Cheers,
Nathan Jones
On Tue, Nov 22, 2011 11:06 AM CST David Katz wrote:
>Nathan,
>I use an SW for backup in AC coupling. I use one of the auxiliary 1 amp relays to activate a larger relay on the AC output of the grid tie inverter to break the Ac connection when the batteries reach full charge voltage. This is I simple but crude pwm charge control merthod. When the AC breaks, the grid tie inverter goes off for 5 minutes. The loads operate on the Sw, pulling the battery down, which closes the relay and the cycle repeats.
>David Katz
>
>----- Original Message -----
>From: Nathan Jones [mailto:solardude97 at yahoo.com]
>Sent: Tuesday, November 22, 2011 07:10 AM
>To: re-wrenches at lists.re-wrenches.org <re-wrenches at lists.re-wrenches.org>
>Subject: Re: [RE-wrenches] Convert Grid Tie SW4048 to Backup System; Add New Inverter, AC Coupled
>
>Bill,
>I believe Allans post indirectly answered my question. While he did not specifically state the SW could be used in an AC coupled arrangement, I believe it was implied. Since the listing issue, as I understand it, was due to failure to drop out of sell mode in a certain set of circumstances and never had anything to do with the behavior of the inverter in any of its "incoming AC only" settings as far as disconnecting there should not be any question as to its suitability for AC coupling there. The only question would be how they would react and manage backfed AC from a GTI in event of a grid failure. That question is unknown to me and has not been specifically answered yet. Any one have an answer to that?
>Nathan Jones
>Power Source Solar
>Springfield, Mo
>R
>417-827-0738
>On Tue, Nov 22, 2011 6:08 AM CST Bill Loesch wrote:
>
>>
>>Fellow Wrenches,
>>
>>Didn't Jim Duncan provide the impetus for the delisting and hasn't he
>>provided a comprehensive discussion here (or some other linked location)
>>before?
>>Does anyone have an answer to Nathan's question of 20 November 11?
>>
>>Bill Loesch
>>
>>----- Original Message -----
>>From: "William Miller" <william at millersolar.com>
>>To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
>>Sent: Sunday, November 20, 2011 1:12 PM
>>Subject: Re: [RE-wrenches] Convert Grid Tie SW4048 to Backup System; Add New
>>Inverter, AC Coupled
>>
>>
>>> Joel:
>>>
>>> I don't belive it was an NEC thing, it was a UL/ETL consideration. This
>>> relates to the NEC only in that it is required to use listed equipment.
>>>
>>> William Miller
>>>
>>>
>>> At 09:21 AM 11/20/2011, you wrote:
>>> >Where in the NEC is the requirement for the GTI interface?
>>>
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Options & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>>
>>
>>_______________________________________________
>>List sponsored by Home Power magazine
>>
>>List Address: RE-wrenches at lists.re-wrenches.org
>>
>>Options & settings:
>>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>List rules & etiquette:
>>www.re-wrenches.org/etiquette.htm
>>
>>Check out participant bios:
>>www.members.re-wrenches.org
>>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
More information about the RE-wrenches
mailing list