Exeltech exeltech at yahoo.com
Sun Oct 23 22:02:09 PDT 2011


Hello William,

It works as long as you tie into just one phase of the three-phase system for the input .. from which you can then derive single-phase output.  A 180 degree shift is also do-able with multiple output windings in the transformer.

Still recovering from SPI.  It was a *long* week.


Dan


--- On Sun, 10/23/11, William Miller <william at millersolar.com> wrote:

From: William Miller <william at millersolar.com>
Subject: Re: [RE-wrenches] Three-phase off-grid
To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Date: Sunday, October 23, 2011, 11:30 PM



Dan:


We are not desiring 120 degrees.  We are desiring 180 degrees, and
it can be derived, and without a Scott-T.  I have done this
recently.


William Miller




At 08:26 PM 10/23/2011, you wrote:

Mac,


You can't get a 120 degree phase shift from a transformer with windings
on a common core.  Two transformers can be combined in a
"Scott-T" configuration" to synthesize a 120 degree shift,
but special transformers are required.  Also, a Scott-T
configuration must be used with closely balanced loads between
phases.


There's an explanation of how a Scott-T topology works at this
link:


http://en.wikipedia.org/wiki/Scott-T_transformer





Dan





--- On Sun, 10/23/11, mac Lewis <maclewis1 at gmail.com>
wrote:



From: mac Lewis <maclewis1 at gmail.com>

Subject: Re: [RE-wrenches] Three-phase off-grid

To: "RE-wrenches"
<re-wrenches at lists.re-wrenches.org>

Date: Sunday, October 23, 2011, 9:02 PM


Wrenches,


Is it a "special" transformer that will give you the 180 deg
phase shift from the original 120 deg shift?


Thanks


On Fri, Oct 21, 2011 at 5:52 PM, William Miller
<william at millersolar.com>
wrote:

Friends:


I posted a question here about three weeks ago on the subject of
connecting a dual SW inverter stack to a three phase generator.  I
have learned a lot since then.  Here are the most important
points:


Most large, three phase generators are allegedly field convertible to
be either 208 or 240 three phase.  The 208 version is probably wye
configured and the phase angle between any two phases is 120
degrees.  If you connect a 120/240 inverter system (even numbers of
Outbacks, two SW's or XWs configured single phase, and maybe other
models) across two of the phases, the 120 degree phasing will cause the
inverters to puke.  If you purchase and connect the correct
transformer across two of these phases and you will provide the 180
degree phase angle you need but you will imbalance the generator. 
For a large (30KVA or larger) generator, the 10 KVA of imbalance is not a
big issue.  Your transformer will cost about $1,000 delivered and
will weigh about 200 pounds.


You can swap some connectors and have a 240 configuration which will
probably have a "stinger" leg.  If it does, the windings
are probably a delta with one winding center tapped.  If so, the
phase angle between the two phases on either side of the neutral is 180
degrees.  You can connect your Outbacks (or others) across these two
phases and neutral without a transformer.  You'e saved your client
$1,000 and yourself a hernia.


If the customer can live with a stinger then you have your cake and
eat it too:  Three phase for 240 VAC loads and a 120/240 single
phase inverter system for 120 or 240 VAC loads.


This realization was huge to me.  Think about it...


William Miller


PS:  Just replacing a 3 phase panel with a single phase panel
does not give you 120/240 with 180 degree phase angle.


Wm








At 08:23 AM 10/21/2011, you
wrote:
Do they actually have 208v loads? If not, replace with 120/240 panel.
Just a thought... Although a transformer would be required to use an
existing 208v generator. 


Jason Szumlanski



On Oct 21, 2011, at 11:17 AM, "Allan Sindelar"
<allan at positiveenergysolar.com>
wrote:



Wrenches,
We have been asked for a design for an off-grid system to reduce
generator runtime for a mountain resort. Initial projections (consumption
measurement results not yet available) suggest 15-20 kW of PV and around
30 kW of inverter capacity. However, the generators and existing wiring
are three-phase 120/208.


My assumption is that our only options are a set of six Sunny
Islands, or 9-12 Outback GVFX3648s. Are there any other options or
approaches that I'm missing?


Thank you, Allan
-- 
A
_______________________________________________
List sponsored by Home Power magazine


List Address:
RE-wrenches at lists.re-wrenches.org


Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules & etiquette:
www.re-wrenches.org/etiquette.htm


Check out participant bios:
www.members.re-wrenches.org









-- 






Mac Lewis


"Yo solo sé que no sé nada."
-Sócrates




-----Inline Attachment Follows-----


_______________________________________________

List sponsored by Home Power magazine


List Address:
RE-wrenches at lists.re-wrenches.org


Options & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules & etiquette:

www.re-wrenches.org/etiquette.htm


Check out participant bios:

www.members.re-wrenches.org_______________________________________________

List sponsored by Home Power magazine


List Address: RE-wrenches at lists.re-wrenches.org


Options & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules & etiquette:

www.re-wrenches.org/etiquette.htm


Check out participant bios:

www.members.re-wrenches.org




No virus found in this incoming message.

Checked by AVG -
www.avg.com 

Version: 8.5.454 / Virus Database: 271.1.1/3970 - Release Date: 10/23/11
18:33:00
 
Miller Solar

Voice :805-438-5600

email: william at millersolar.com

http://millersolar.com

License No. C-10-773985



-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20111023/75916d46/attachment-0004.html>


More information about the RE-wrenches mailing list