[RE-wrenches] Three-phase off-grid
Gary Willett
gary at icarussolarservices.com
Fri Oct 21 13:01:42 PDT 2011
Allan:
Also, you might consider using six to nine Schneider/Xantrex XW6048
inverters, or six to nine Outback Radian GS8048 inverters, in a 3-phase
configuration, with a common battery bank.
Also, Schneider/Xantrex has an 80A 600V charge controller that may be
advantageous depending on the distance from the PV arrays to the inverters.
Regards,
Gary Willett, PE
Icarus-Engineering LLC
Icarus Solar Services LLC
On 10/21/2011 10:17, Allan Sindelar wrote:
> Wrenches,
> We have been asked for a design for an off-grid system to reduce
> generator runtime for a mountain resort. Initial projections
> (consumption measurement results not yet available) suggest 15-20 kW
> of PV and around 30 kW of inverter capacity. However, the generators
> and existing wiring are three-phase 120/208.
>
> My assumption is that our only options are a set of six Sunny Islands,
> or 9-12 Outback GVFX3648s. Are there any other options or approaches
> that I'm missing?
>
> Thank you, Allan
> --
> *Allan Sindelar*
> _Allan at positiveenergysolar.com_ <mailto:Allan at positiveenergysolar.com>
> NABCEP Certified Photovoltaic Installer
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> *Positive Energy, Inc.*
> 3201 Calle Marie
> Santa Fe, New Mexico 87507
> *505 424-1112*
> _www.positiveenergysolar.com_ <http://www.positiveenergysolar.com/>
>
> *
> *
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options& settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules& etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20111021/9e8dc06b/attachment-0003.html>
More information about the RE-wrenches
mailing list