Connectors were fully engaged. I would also think what you described would cause an AC short, at least intermittently, in the connector. GFI tripping is a DC problem. It worked fine for 5 months until a week ago.

Kirk Herander
VSE

On Jun 17, 2011, at 12:27 PM, "Mark Frye" <markf at berkeleysolar.com> wrote:

> I see.
>  
> My experience with the M190 ac connector is this: It is possible to join the two connector halves and rotate the cuff sufficiently to establish an electrical connection. But if you don't rotate the cuff until the detant is engaged, you may not completely seal the connection by compressing the internal face gasket.
>  
> I really haven't looked into it much further but I wonder if the water you observed entered through an incomplete connector mate, along the conductors, into the inverter enclosure?
> 
> Mark Frye 
> Berkeley Solar Electric Systems 
> 303 Redbud Way 
> Nevada City,  CA 95959 
> (530) 401-8024 
> www.berkeleysolar.com 
> 
>  
> 
> From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Kirk Herander
> Sent: Friday, June 17, 2011 4:51 AM
> To: 'RE-wrenches'
> Subject: Re: [RE-wrenches] Enphase Nema 6 enclosure - not
> 
> yes
> 
>  
> 
> Kirk Herander
> 
> VT solar, LLC
> 
> dba Vermont Solar Engineering
> 
> NABCEPTM Certified installer Charter Member
> 
> NYSERDA-eligible Installer
> 
> VT RE Incentive Program Partner
> 
>  
> 
> From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mark Frye
> Sent: Thursday, June 16, 2011 11:28 PM
> To: 'RE-wrenches'
> Subject: Re: [RE-wrenches] Enphase Nema 6 enclosure - not
> 
>  
> 
> Was that an M190?
> 
> 
> Mark Frye 
> Berkeley Solar Electric Systems 
> 303 Redbud Way 
> Nevada City,  CA 95959 
> (530) 401-8024 
> www.berkeleysolar.com 
> 
>  
> 
>  
> 
> From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Kirk Herander, VSE
> Sent: Thursday, June 16, 2011 6:50 PM
> To: 'RE-wrenches'
> Subject: [RE-wrenches] Enphase Nema 6 enclosure - not
> 
> I just figured out why I could not reset a GFI error on one of my micro-inverters. First, I noticed condensation in the led lens, then water literally dripped out of the AC side as soon as I disconnected it. This was mounted on the top backside of a panel, roughly two ft above a flat roof. ….. fascinating
> 
>  
> 
> Kirk Herander
> 
> Vermont Solar Engineering
> 
> 802.863.1202  fax 802.863.7908
> 
> VT RE Incentive Program  Partner
> 
> NYSERDA Incentive-eligible Partner
> 
> NABCEPTM    Certified Installer
> 
>  
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110617/249cccd1/attachment-0004.html>


More information about the RE-wrenches mailing list