[RE-wrenches] Xantrex 3 XW system bypass
Gary Willett
icarussolar at verizon.net
Mon May 16 15:12:43 PDT 2011
Jason:
A possible solution might be a 3-pole / 3-wire manual transfer switch,
or an automatic transfer switch that has manual transfer capability.
If the three Xantrex XW inverters are in a WYE configuration and set up
as a "separately derived system", you will need a 4-pole / 4-wire ATS so
the neutral can be switched too.
Put the 3-phase grid connection on the "utility in" of the ATS
Put the 3-phase service panel on the "load out" of the ATS
Put the Xantrex 3-phase AC outputs on the "generator in" side of the ATS
Here are some sources you may want to peruse:
EMERSON / ASCO:
http://www.emersonnetworkpower.com/en-US/Products/PowerSwitchingandControls/PowerTransferSwitches/Pages/default.aspx
GENERAL ELECTRIC:
http://www.gedigitalenergy.com/powerquality/ATSHome.htm
RONK: http://www.ronkelectrical.com/pdfstech/METERRITE%20GL.pdf
EATON / CUTLER-HAMMER:
http://www.eaton.com/Electrical/USA/ProductsandServices/ElectricalDistribution/ATS/index.htm
Regards,
Gary Willett, PE
Icarus Engineering / Solar Services LLC
NABCEP Certified Solar PV Installer # 031310-246
<mailto:Gary at IcarusSolarServices.com>
On 5/16/2011 3:34 PM, Jason Szumlanski wrote:
> I am looking for an external output bypass assembly for a Xantrex 3 x
> XW4024 system. My customer wants to be able to completely bypass the
> inverter output and operate loads straight from the grid - similar to
> what can be done in an Outback FlexWare system with their I/O bypass
> assemblies.
>
> This customer just wants the option of running loads direct from
> utility. It has nothing to do with the inverter input side.
>
> Any off-the-shelf solutions out there?
>
> Jason Szumlanski
> Fafco Solar
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options& settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules& etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110516/fb0c745b/attachment-0004.html>
More information about the RE-wrenches
mailing list