Thu Mar 24 15:55:06 PDT 2011
Hey Dana, it's EQ then top off.
Rob
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dana
Sent: Thursday, March 24, 2011 1:35 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Testing new batteries
HUP Solar One batteries recommend topping off the electrolyte and doing an
initial EQ cycle prior to use. We always check SG and voltage/cell on
arrival and to date never had any discrepancy on either.
Additionally we unbolt all connections, polish with a copper pipe wire brush
all connecting surfaces [with a respirator on] re-bolt, check voltage & SG,
then coat with Vaseline all connecting surfaces.
So, total we check volt per cell and SG twice. Considering that this bank
will be in place for 16-20 years it is a good place to start. Do it once and
do it correctly. This serves as a good baseline.
I have mentioned this before but we only use a refractometer for checking
specific gravity anymore the accuracy is dead on and not subject to sticking
floats and curvature of the electrolyte in the hydrometer. Refractometers
are $85-$100 each from a good plumbing wholesale house.
Dana Orzel
Great Solar Works, Inc
E - dana at solarwork.com
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076
web - www.solarwork.com
"Responsible Technologies for Responsible People since 1988"
Do not ever believe anything, but seriously trust through action.
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Nick Soleil
Sent: Thursday, March 24, 2011 11:20 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Testing new batteries
Hi Benn:
Perhaps those batteries have just been sitting a little while, and need
a recharge. Generally speaking, if you find that the batteries test reading
are a little low, they are probably just a little discharged. After
recharging the batteries, test them again. If those readings are low, then
contact the manufacturer with the data. I have had great luck with battery
manufacturers warranting their defective batteries in warranty.
Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037
_____
From: benn kilburn <benn at daystarsolar.ca>
To: Wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Thu, March 24, 2011 9:43:20 AM
Subject: [RE-wrenches] Testing new batteries
I'm curious of others experiences with testing "new" batteries right from
the mfgr, before putting them into service. I'm not talking about load
testing, i mean just basics...voltage, specific gravity and electrolyte
level.
I recently received some batteries (24 x 2V) and before putting them to work
i tested all the voltages, SG's and levels. Voltages were all with-in 0.016
V (2.1-2.084). The SG's were within 0.037 (1.281-1.244). Yes, the one with
the lowest SG also had the lowest V.
What concerns me a bit more than the few cells with lower SG is the
consistent low levels of electrolyte. All cells were between 3/4" and
1-1/2" below full, which is 1/4" below the bottom of the vent well tube....
with one exception that was bang-on full. Interestingly, the one full
battery was the only one with a different date code than the rest.
Should the various levels of electrolyte mentioned be acceptable when a
battery is brand new, straight from the mfgr? How bout the SG's?
I'm considering adding electrolyte from a local battery shop instead of
distilled water to top up all the batteries. Comments?
Very thankful for the wealth of knowledge and experience on this list,
benn