HUP Solar One batteries recommend topping off the
electrolyte and doing an initial EQ cycle prior to use. We
always check SG and voltage/cell on arrival and to date
never had any discrepancy on either.

 

Additionally we unbolt all connections, polish with a copper
pipe wire brush all connecting surfaces [with a respirator
on] re-bolt, check voltage & SG, then coat with Vaseline all
connecting surfaces.

 

So, total we check volt per cell and SG twice. Considering
that this bank will be in place for 16-20 years it is a good
place to start. Do it once and do it correctly. This serves
as a good baseline. 

 

I have mentioned this before but we only use a refractometer
for checking specific gravity anymore the accuracy is dead
on and not subject to sticking floats and curvature of the
electrolyte in the hydrometer.  Refractometers are $85-$100
each from a good plumbing wholesale house.

 

Dana Orzel

Great Solar Works, Inc

E - dana at solarwork.com

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

web - www.solarwork.com

 

"Responsible Technologies for Responsible People since 1988"

Do not ever believe anything, but seriously trust through
action.

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf
Of Nick Soleil
Sent: Thursday, March 24, 2011 11:20 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Testing new batteries

 

Hi Benn:
    Perhaps those batteries have just been sitting a little
while, and need a recharge.  Generally speaking, if you find
that the batteries test reading are a little low, they are
probably just a little discharged.  After recharging the
batteries, test them again.  If those readings are low, then
contact the manufacturer with the data.  I have had great
luck with battery manufacturers warranting their defective
batteries in warranty.

 

Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037

 

 

  _____  

From: benn kilburn <benn at daystarsolar.ca>
To: Wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Thu, March 24, 2011 9:43:20 AM
Subject: [RE-wrenches] Testing new batteries

I'm curious of others experiences with testing "new"
batteries right from the mfgr, before putting them into
service.  I'm not talking about load testing, i mean just
basics...voltage, specific gravity and electrolyte level.

 

I recently received some batteries (24 x 2V) and before
putting them to work i tested all the voltages, SG's and
levels.  Voltages were all with-in 0.016 V (2.1-2.084).  The
SG's were within 0.037 (1.281-1.244).  Yes, the one with the
lowest SG also had the lowest V.  

 

What concerns me a bit more than the few cells with lower SG
is the consistent low levels of electrolyte.  All cells were
between 3/4" and 1-1/2" below full, which is 1/4" below the
bottom of the vent well tube.... with one exception that was
bang-on full.  Interestingly, the one full battery was the
only one with a different date code than the rest. 

 

Should the various levels of electrolyte mentioned be
acceptable when a battery is brand new, straight from the
mfgr?  How bout the SG's?

 

I'm considering adding electrolyte from a local battery shop
instead of distilled water to top up all the batteries.
Comments?

 

Very thankful for the wealth of knowledge and experience on
this list,

benn