[RE-wrenches] Meter base minimum conductor size
Louis Woofenden
louis at woofenden.net
Wed Feb 9 16:55:50 PST 2011
Hi Carl,
We use Cooper B-Line meter bases for this application. The 100A meter
base terminals are good from #14AWG to 2/0AWG. Check out
<http://cooperbline.com/product/PDFLibrary/metermountingequipment/index.htm>,
click on "Single Meter Sockets -- Without Bypass," on the left, then
click on "100 Amp Self-Contained."
We sometimes have to special order these, but they aren't too pricey, as
far as I recall.
Best,
Louis Woofenden
Net Zero Solar
Tucson, AZ
On 2/9/11 5:23 PM, Carl Adams wrote:
> We often use a conventional 100A meter base and analog meter as an
> independent metering system for inverter output. These meters
> typically have a minimum conductor size of #6 AWG. For smaller
> systems the inverter output conductors are smaller than #6 AWG...