They did provide us with an installation manual. In talking with their
technicians they have told us that there are hundreds of other similar
installations of their equipment around the world and that they have not
seen anything like this problem anywhere else. They did offer to refund
our money and simply turn off the data connection to the combiner boxes.
However, our client, who happens to be an electrical engineer, would like
to have the system fixed.



> Hi Vince,
>
> I don't know anything about Energy Recommerce, but a search of their
> website did
> not result in finding an installation manual for their combiner box, only
> a
> datasheet. You stated countless hours were spent on the phone with their
> technicians. If it was my job, at this point, I would want my money back.
> If
> it's that hard to fix, it's worse than worthless, it's costing you
> bundles.
>
> Dick Ratico
> Solarwind Electric
>
>
> --- You wrote:
> Sorry for the long post. I don't know how else to communicate this issue.
> We installed an Energy Recommerce data system on a project last year that
> we have not been able get working properly. Everything works except the
> monitoring of the series string amperage outputs from the solar array.
> There are 3 pv source circuit combiner boxes with 11 series strings of 14
> modules and 1 with 10 series strings of 14. Each combiner box feeds one
> inverter with its own conduit run. The data system shows amperage from
> each circuit consistent within each combiner box, typically with a range
> of variance of about 1.5 amps DC between series strings.  Each combiner
> box will show totally divergent amperages. For example, combiner box 1
> might read 2 amps, combiner box 3 reads 10 amps, and at the same time our
> clamp meters are reading the actual amperage at around 5 amps consistently
> between every box for every circuit. The same combiner boxes will
> consistently read either too low or too high. The problem may be in the
> interface between the Hall Effect sensors that the circuit board in the
> combiner box uses to measure the DC current. The Hall Effect sensors
> deliver a calibrated voltage based on the strength of the magnetic field
> around the series string circuit as it goes through the box. The combiner
> box then calculates the amperage based on the millivolts that the Hall
> Effect sensor produces. For example 500 millivolts equals 5 amps.  The DC
> output voltage of the Hall Effect sensor varies by about 50 millivolts or
> more, so rapidly that it$E2s hard for our meters to follow it. We have
> spent
> countless hours on the phone with Energy Recommerce technicians trying
> everything that anyone could think of to trouble shoot the problem. Their
> system uses a MODBUS protocol for transferring the data and there seems to
> be no problem with the data transmission or connectivity.  I would love to
> hear from anyone that sees a pattern to this problem that might help us
> find a solution.
> --- end of quote ---
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>





More information about the RE-wrenches mailing list