[RE-wrenches] calculating low string voltage
boB at midnitesolar.com
boB at midnitesolar.com
Tue Nov 29 22:02:30 PST 2011
If you really want to throw a monkey wrench into the mix, bring up
partial shading...
Or, maybe that's just not allowed in that debate ?? Just a thought.
boB
On 11/29/2011 8:39 PM, Kent Osterberg wrote:
> Kirk,
>
> You've got some good feedback on this from Ray and Bill. I'll try to
> add a little more. Most module datasheets show a normal operating cell
> temperature, NOCT, value that's typically 47.5°C. That's 20°C ambient
> temperature, 800 W/sq m, and calm wind and nothing blocking the
> airflow on the back of the module. That 27.5°C temperature rise should
> be pretty close to the temperature rise that occurs for a pole-top
> mount. It's common to see people use 25°C for modules on a pole and
> 30°C or 35°C on a roof and there are data that support these "typical"
> values. With 1000 W/sq irradiance, the temperature rise can obviously
> be more too. Between the intensity of the sun, the direction of the
> sun, the color of the roof, the spacing off the roof, and the wind
> speed there is a lot that is different from one system to the next or
> even one day to the next.
>
> Most PV module spec sheets don't give you a temperature coefficient
> for Vmp. I've seen people use the the Voc coefficient, usually
> expressed as a percentage, for both Voc and Vmp. Big mistake. Data
> from NREL indicates as Bill said, the temperature coefficient for Vmp
> is higher than that the temperature coefficient for Voc. That's
> particularly true when the coefficient is expressed as a percentage
> per °C. Since there are very few manufacturer's that give both
> temperature coefficients, I'll use a value from an old Evergreen
> module for an example. The Evergreen ES-195 datasheet shows Voc = 30.5
> volts with a coefficient of -0.34%/°C and Vmp = 27.1 volts with a
> coefficient of -0.47%/°C. Since one shouldn't add volts and percents,
> I'll put the temperature coefficients in volts/°C: Voc = 30.5 V - 0.10
> V/°C and Vmp = 27.1 V - 0.13V/°C. So Vmp is moving faster than Voc,
> but not a lot faster. That's generically true for c-Si or poly-Si.
> Kent Osterberg
> Blue Mountain Solar, Inc.
> www.bluemountainsolar.com
> t: 541-568-4882
>
> On 11/29/2011 11:48 AM, Kirk Herander wrote:
>>
>> I am in debate with a PE over calculation of low voltage of a series
>> string on a hot day. He insists that an arbitrary high cell temp is
>> factored in, not just ambient temperature. Could someone please give
>> an accepted formula for this calculation? Thanks. I cannot find a
>> clear reference to low voltage calculation on a hot day (but every
>> reference material is clear on how to calculate high voltage on a
>> cold day).
>>
>> Kirk Herander
>>
>> VT Solar, LLC
>>
>> dba Vermont Solar Engineering
>>
>> NABCEP^TM Certified installer Charter Member
>>
>> NYSERDA-eligible Installer
>>
>> VT RE Incentive Program Partner
>>
>>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options& settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules& etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20111129/834e2154/attachment-0003.html>
More information about the RE-wrenches
mailing list