[RE-wrenches] High-power MPPT/Charge Controllers?
Darryl Thayer
daryl_solar at yahoo.com
Sat Nov 19 08:20:51 PST 2011
Hi
I have a system in operation since 2003 using 13 paralleled Outback MX 60 CC and I have measured over 600 Amps at 48 Volts.on the common bus. Outback and I replaced the fans in the MX 60s but we have had no failures. This power is converted to 60 hZ using 12 Outback inverters, I have had an inverter trip off on the DC side just the other day and I will check it out this comming week but no problems.
DT
________________________________
From: "Larry Crutcher, Starlight Solar Power Systems" <larry at starlightsolar.com>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Friday, November 18, 2011 12:35 PM
Subject: Re: [RE-wrenches] High-power MPPT/Charge Controllers?
Sounds like a project for Sunny Island and the Boy's.
Larry Crutcher
Starlight Solar Power Systems
On Nov 18, 2011, at 10:49 AM, Exeltech wrote:
Need info on MPPT/charge controllers able to output up to 500A at 48Vdc.
>High-voltage DC input (up to 300Vdc) preferred. Units will connect to a
>20-24 kW PV array and 150 kW-h battery for a large off-grid system.
>Not locked into 48Vdc. Can go up to 108Vdc (nominal) if needed.
>
>Any such CC units available?
>
>If not, what's been the collective Wrench experience in paralleling multiple
>controllers of whatever max output amperage exists on the market? I realize
>a paralleled configuration of this nature would entail multiple separate arrays
>in use on the input. That won't be a problem. Just need to be able to feed
>the common battery bank.
>
>Thanks.
>
>Dan
>
> _______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>_______________________________________________List sponsored by Home Power magazineList Address: RE-wrenches at lists.re-wrenches.orgOptions & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:www.re-wrenches.org/etiquette.htmCheck out participant bios:www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20111119/4aa7ec9e/attachment-0003.html>
More information about the RE-wrenches
mailing list