[RE-wrenches] High Voltage MPPT units; Adding battery backup
Drake
drake.chamberlin at redwoodalliance.org
Thu Nov 10 04:56:58 PST 2011
The GENTRAN sounds very interesting. The Internet has some for sale,
but so far no detail. Will the 12 circuit panel shed one circuit at
a time? In a nutshell, how does this work?
Thanks,
Drake
At 02:32 AM 11/10/2011, you wrote:
>Hi Wrenchies,
>
>Yes and if you use a GENTRAN or equivalent circuit-by-circuit
>transfer switch add-on for the output from the offgrid inverter to
>your AC panel - then there is no need for a separate dedicated AC
>loads panel and rewire like in Larry's original drawing. I've used
>this trick for years to avoid a dedicated subpanel for the output of
>an off-grid inverter. Combined with the DC transfer switch idea
>that high voltage MPPTs enable, (we've been waiting for this) you
>have a really simple retrofit for an on-grid system.
>
>And now with Magnum and others offering low-power 120/240 split
>phase outputs in one inverter - the grid-tie hybrid retrofit market
>is getting more attractive all the time. DC Transfer Switch to MPPT
>Charger to 120/240 split phase inverter/battery to GENTRAN
>Switch. Getting cheaper all the time.
>
>And hopefully one day not too far off SMA will bring their "Backup
>Set S" they show in their European catalog to the States- this is
>basically a 2.2 KW version of the Sunny Island - 2 of them would
>achieve 120/240 stacked and be a nice cheaper SB enabler as well.
>
>Also your standard 100 AMP 4 pole DPDT transfer switch may not be
>rated for 600 VDC explicitly but think of it - the old knife style
>units "throw" is like 12" - no way that won't work with 600 VDC.
>
>Hope that helps!,
>
>Jeff
>
>
>
>
>
>Larry Crutcher, Starlight Solar Power Systems wrote:
>>
>>Right.... a major rewire and many components...and sacrifices. The
>>Outback is limited to 30 amps AC and cost much more than you would
>>need to spend.
>>
>>With my idea you just add a transfer switch....Done. When the grid
>>is down, PV feeds HV CC. Then you can use ANY size inverter, with
>>or without a transfer switch. No rewiring the grid inverter. No 240
>>volt transformers or dual inverters. No relays, switches or
>>diversion controllers. Batteries are always properly maintained. No
>>phantom loads. Very simple.
>>
>>Thanks for your input. Now if I can just find that darn 600 volt
>>transfer switch.
>>
>>Larry Crutcher
>>Starlight Solar Power Systems
>>
>>
>>
>>On Nov 9, 2011, at 1:55 PM, Drake wrote:
>>
>>>
>>>Any amount of power will AC couple.
>>>
>>>If you use an off grid inverter, such as an Outback, to feed the
>>>protected load panel, the inverter should be fed by grid AC power
>>>to supply loads, when the grid is available. Just feed your grid
>>>tie inverter into the protected loads panel. You will need a
>>>relay to shut off power from the grid tie inverter when the
>>>batteries are full. This can be triggered by the fan relay in the Outback.
>>>
>>>The on grid inverter will push power into the grid through the
>>>battery inverter's internal transfer switch during normal
>>>operation and AC couple when the power is out. If your grid tie
>>>inverter is 240 volts, you will need to use a transformer or two inverters.
>>>
>>>The phantom load of the inverter can be eliminated by using a
>>>transfer switch to send PV power straight to the grid, during
>>>normal grid availability, keeping the inverter turned off. AC
>>>coupling seems much easier than using a charge controller, but
>>>there is no conditioning of the batteries. The charge is just on
>>>and off at the voltage set point. For a back up system, that is
>>>not much of a problem, as the battery inverter can maintain the
>>>batteries when power is available.
>>>
>>>
>>>
>>>At 02:04 PM 11/9/2011, you wrote:
>>>>
>>>>Nice Find, Drake! Thanks.
>>>>
>>>>What is the minimum system for an AC coupled inverter?
>>>>
>>>>Again, the idea is for low cost battery backup of an existing
>>>>grid tie. The AC coupled schematics I have looked at require a
>>>>major rewire and many components. I would like to hear if someone
>>>>has a simple add on solution compared to just switching the array
>>>>to the high voltage CC.
>>>>
>>>>Larry Crutcher
>>>>Starlight Solar Power Systems
>>
>>_______________________________________________
>>List sponsored by Home Power magazine
>>
>>List Address:
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Options & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive:
>><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>List rules & etiquette:
>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>
>>Check out participant bios:
>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>>
>>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
Drake Chamberlin
ATHENS ELECTRIC LLC
OH License 44810
CO license 3773
NABCEP Certified PV
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20111110/4a6d4f73/attachment-0003.html>
More information about the RE-wrenches
mailing list