[RE-wrenches] Wet locations: (was Push-in Wire Connectors)
Ray Walters
ray at solarray.com
Fri Oct 21 16:08:15 PDT 2011
I started using the wet rated wire nuts, because I've found some
corrosion in old connectors in outdoor boxes. BTW, why don't you like
the goo filled wire nuts? They seem a decent and cost effective solution.
I agree with your idea that condensation and moisture buildup can
occur even in a NEMA 4 box, and the issue that I have is that breakers
and fuse holders in combiner boxes are definitely not wet rated. I
wonder what happens to the internal workings of a breaker after decades
in an outdoor box, but considering there are an awful lot of them around
(at least AC) I guess I'll get another night's sleep in our less than
perfect world of PV wiring.
Ray
On 10/21/2011 9:05 AM, Jamie Johnson wrote:
> William, the only explanation that I have found for using THWN-2 in
> conduit run through the attic is that during the day as the
> temperature in the attic increases, the air in the conduit expands, at
> night the opposite effect happens, the temperature in the attic
> decreases and the volume of air in the conduit contracts with the
> potential to bring in what ever climate conditions exist outside the
> conduit (In FL this could be humid air).
> Over time if there is humid air present, this could form condensation
> in the conduit or NEMA 4 rated enclosure, hence the need for wire and
> connections rated for a wet location.
> I have seen photos at inspectors meetings of NEMA 4 enclosures and
> conduit that contained water although I am not sure how often this
> would normally happen.
>
> *Jamie Johnson
> NABCEP Certified PV Technical Sales Professional
> NABCEP Certified Solar PV Installer
>
> General Manager*
> *SOLAR POWER ELECTRIC*
> **
> **
>
> -------- Original Message --------
> Subject: [RE-wrenches] Wet locations: (was Push-in Wire Connectors)
> From: William Miller <william at millersolar.com
> <mailto:william at millersolar.com>>
> Date: Fri, October 21, 2011 10:51 am
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org
> <mailto:re-wrenches at lists.re-wrenches.org>>
>
> Friends:
>
> I have had plan checkers insist I use wet rated wire on rooftops
> even though the wire was in either liquid tight or EMT with
> raintight connectors. I did not need to dispute this because we
> had specified THHN wire that is also rated THWN for wet
> locations. This discussion makes me think I should have
> contradicted the requirement because I am not sure wet rated wire
> is required inside dry conduit. I will be looking this up.
>
> I feel that you should not let an AHJ impose a requirement that is
> not in the code because then you become bound to the new
> stricture. I realize that an AHJ can impose stricter
> requirements, but I insist that it be in writing, required in
> advance of the job in question and that it be required
> universally. Otherwise, it's anarchy.
>
> William Miller
>
>
> Miller Solar
> Voice :805-438-5600
> email: william at millersolar.com <mailto:william at millersolar.com>
> http://millersolar.com
> <http://millersolar.com/>License No. C-10-773985
>
> ------------------------------------------------------------------------
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options& settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules& etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20111021/6c9e09ec/attachment-0003.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 12045 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20111021/6c9e09ec/attachment-0003.jpe>
More information about the RE-wrenches
mailing list