    I started using the wet rated wire nuts, because I've found some
    corrosion in old connectors in outdoor boxes. BTW, why don't you
    like the goo filled wire nuts? They seem a decent and cost effective
    solution.<br>
     I agree with your idea that condensation and moisture buildup can
    occur even in a NEMA 4 box, and the issue that I have is that
    breakers and fuse holders in combiner boxes are definitely not wet
    rated. I wonder what happens to the internal workings of a breaker
    after decades in an outdoor box, but considering there are an awful
    lot of them around (at least AC) I guess I'll get  another night's
    sleep in our less than perfect world of PV wiring.<br>
    <br>
    Ray<br>
    <br>
    On 10/21/2011 9:05 AM, Jamie Johnson wrote:
    <blockquote
cite="mid:20111021080507.cbd8bec484907cf1a9d3a5fb1ad0b5d1.fa84f31d96.wbe@email03.secureserver.net"
      type="cite"><span style="font-family:Verdana; color:#000000;
        font-size:10pt;">
        <div>William, the only explanation that I have found for using
          THWN-2 in conduit run through the attic is that during the day
          as the temperature in the attic increases, the air in the
          conduit expands, at night the opposite effect happens, the
          temperature in the attic decreases and the volume of air in
          the conduit contracts with the potential to bring in what ever
          climate conditions exist outside the conduit (In FL this could
          be humid air).</div>
        <div> </div>
        <div>Over time if there is humid air present, this could form
          condensation in the conduit or NEMA 4 rated enclosure, hence
          the need for wire and connections rated for a wet location.</div>
        <div> </div>
        <div>I have seen photos at inspectors meetings of NEMA 4
          enclosures and conduit that contained water although I am not
          sure how often this would normally happen.<br>
        </div>
        <div><br>
        </div>
        <div><span style="FONT-SIZE: 8pt"><span style="COLOR: #3366ff"><strong><span
                  style="COLOR: #0000ff">Jamie Johnson<br>
                  NABCEP Certified PV Technical Sales Professional<br>
                  NABCEP Certified Solar PV Installer<br>
                  <br>
                  General Manager</span></strong></span></span></div>
        <div><span style="FONT-SIZE: 8pt"><span style="COLOR: #3366ff"><strong><span
                  style="COLOR: #0000ff">SOLAR POWER ELECTRIC</span></strong></span></span></div>
        <div><span style="FONT-SIZE: 8pt"><span style="COLOR: #3366ff"><strong></strong></span></span></div>
        <div><span style="FONT-SIZE: 8pt"><span style="COLOR: #3366ff"><strong><span
                  style="COLOR: #0000ff"><img title="signature image"
                    alt=""
                    src="cid:part1.09030106.00020307@solarray.com"
                    border="0"></span></strong></span></span></div>
        <div> </div>
        <div> </div>
        <blockquote style="BORDER-LEFT: blue 2px solid; PADDING-LEFT:
          8px; FONT-FAMILY: verdana; COLOR: black; MARGIN-LEFT: 8px;
          FONT-SIZE: 10pt" id="replyBlockquote" webmail="1">
          <div id="wmQuoteWrapper">-------- Original Message --------<br>
            Subject: [RE-wrenches] Wet locations: (was Push-in Wire
            Connectors)<br>
            From: William Miller <<a moz-do-not-send="true"
              href="mailto:william@millersolar.com">william@millersolar.com</a>><br>
            Date: Fri, October 21, 2011 10:51 am<br>
            To: RE-wrenches <<a moz-do-not-send="true"
              href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>><br>
            <br>
            <x-sigsep>
              <p><font size="3">Friends:<br>
                  <br>
                  I have had plan checkers insist I use wet rated wire
                  on rooftops even though the wire was in either liquid
                  tight or EMT with raintight connectors.  I did not
                  need to dispute this because we had specified THHN
                  wire that is also rated THWN for wet locations.  This
                  discussion makes me think I should have contradicted
                  the requirement because I am not sure wet rated wire
                  is required inside dry conduit.  I will be looking
                  this up.<br>
                  <br>
                  I feel that you should not let an AHJ impose a
                  requirement that is not in the code because then you
                  become bound to the new stricture.  I realize that an
                  AHJ can impose stricter requirements, but I insist
                  that it be in writing, required in advance of the job
                  in question and that it be required universally. 
                  Otherwise, it's anarchy.<br>
                  <br>
                  William Miller<br>
                  <br>
                  <br>
                  Miller Solar<br>
                  Voice :805-438-5600<br>
                  email: <a moz-do-not-send="true"
                    href="mailto:william@millersolar.com">william@millersolar.com</a><br>
                  <a moz-do-not-send="true"
                    href="http://millersolar.com/" target="_blank"
                    eudora="autourl">http://millersolar.com<br>
                  </a>License No. C-10-773985<br>
                </font>
              </p>
              <hr>
              _______________________________________________<br>
              List sponsored by Home Power magazine<br>
              <br>
              List Address: <a moz-do-not-send="true"
                href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
              <br>
              Options & settings:<br>
              <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
              <br>
              List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
              <br>
              List rules & etiquette:<br>
              <a moz-do-not-send="true"
                href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
              <br>
              Check out participant bios:<br>
              <a moz-do-not-send="true"
                href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>
              <br>
            </x-sigsep></div>
        </blockquote>
      </span>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>