[RE-wrenches] Adding on to existing PV System

Mark Frye markf at berkeleysolar.com
Thu Sep 29 13:18:41 PDT 2011


Jason:
 
SB 5000 = 21A @ 240V, 21A x 1.25 = 26.3A needs 30A breaker
M215 = 0.9 A @ 240V, 0.9A x 9 = 8.1 A, 8.1 x 1.25 = 10.1A needs 15A breaker.
(Or that rounded to 10A and use a 10A breaker)?
 
26.3A + 10.1A = 36.4 A needs 40A breaker
 
So, get a new 100A main lug subpanel. Connect it to a 40A breaker in the
existing main panel. Move the existing 30A breaker into the new subpanel and
install the new 15A breaker into the same.

Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 <http://www.berkeleysolar.com/> www.berkeleysolar.com  
 

  _____  

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Thursday, September 29, 2011 12:55 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Adding on to existing PV System



That's not a bad idea, except that 690.64(B)(2) requires that the breaker
directly connected to each inverter(s) must be used for the calculation.

 

I have an existing SB5000 with a 30A breaker and a new string of nine
Enphase M215's requiring a 15A breaker. If you combine these in a 100A or
higher rated subpanel with a 40A main breaker, you still calculate the total
current supplying the busbar in the main distribution panel based on 200A +
30A + 15A = 245A (with 30A and 15A being the overcurrent protection directly
connected to the inverters). This exceeds the 120% rule by 5A. It also
requires that the ampacity of the conductors between the two panels be 85A /
1.2 = 70.83A (assuming a 40A backfeed breaker in the main distribution
panel). If your interpretation is different, please let me know!

 

If my interpretation is correct, I like the idea of just adding a fusible
disconnect and using #10 conductors all the way to the tap. That would be
the most cost effective solution I believe, and since there is no
foreseeable further system rating increases, the advantage of a subpanel is
reduced.

 

 

Thanks for all the other suggestions provided. Unfortunately I can't put in
smaller main breaker, and the busbar in the main panel is definitely rated
200A.

 

Jason Szumlanski

Fafco Solar

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Glenn Burt
Sent: Thursday, September 29, 2011 2:40 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Adding on to existing PV System

 

How about feeding both systems into an AC combining subpanel before feeding
the main load center?

Often the calculations required will allow you to do more backfeeding than
the simple backfeeding a load center with individual breakers.

 

-Glenn

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Thursday, September 29, 2011 11:49 AM
To: RE-wrenches
Subject: [RE-wrenches] Adding on to existing PV System

 

We've been contracted to add on to an existing PV system in a residence. The
existing system has a 30A 2P Breaker on a 200A rated panel with a 200A main
breaker. The new system would require a 15A breaker, which would exceed the
limit in NEC 690.64(B)(2).

 

The existing system has a fusible AC disconnect mounted next to the meter.
This was originally intended as the utility external disconnect. The utility
no longer requires a disconnect, but if we do a supply side connection, we
would need a fusible AC disconnect anyway for the new system. I would
collocate the new disconnect with the old.

 

Does anyone see any problem with doing a supply size connection for the new
system? Any labeling snags that I might need to consider?

 

Jason Szumlanski

Fafco Solar

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110929/98d705a5/attachment-0003.html>


More information about the RE-wrenches mailing list