[RE-wrenches] Grounding system for a shack on a frozen lake?
Jason Szumlanski
Jason at fafcosolar.com
Tue Aug 9 09:49:53 PDT 2011
It sounds like you want an AC system for your "home theater" system, so make sure you get a mobile rated inverter if you plan to have a backup AC source. That way you will have integral neutral-ground bond switching. The mobile versions are rarely much more $, if at all. Try Magnum or Outback.
And make sure you plan for a satellite dish so you can pick up curling matches.
Jason Szumlanski
On Aug 9, 2011, at 9:09 AM, "Exeltech" <exeltech at yahoo.com> wrote:
> First .. why are you grounding a portable system? It's not required.
>
> In [29 CFR 1926.404(f)(3)(i)], OSHA states the frame of a portable
> generator need not be grounded (connected to earth).
>
> If it's a fuel-powered generator, the NEC 250.34 states the frame may
> serve as the ground as long as normally non-current-carrying metal parts
> of equipment and the equipment grounding conductor terminals of the
> receptacles are connected to the generator frame.
>
> This is even more applicable if the system is all low-voltage DC only.
>
>
> Dan
>
>