[RE-wrenches] 2 SW inverters on three phase
boB Gudgel
boB at midnitesolar.com
Thu Jul 28 10:56:07 PDT 2011
Do you just want to charge batteries and are these regular 120VAC SWs
?? 120/208 ??
If so, you should just be able to connect each SW from neutral to hot.
No stacking necessary.
A regular SW stacking cable won't work for delta connections because
that assumes
the phases are going to be 180 degrees (120/240) and not 120 degrees as
for 208V delta.
There was a 3 phase version of the SWs which required a separate 3-way
cable and
different software in the SW itself.
boB
> On Thu, Jul 28, 2011 at 12:23 AM, William Miller
> <william at millersolar.com <mailto:william at millersolar.com>> wrote:
>
> Friends:
>
> Is there any way to connect two SW series inverters to two phases
> of a three phase generator? It seems to me that one could connect
> three SW inverters with the right stacking cable (or am I
> confusing Outback inverters with the hub jumper set properly).
>
> Any input is appreciated.
>
> Thanks,
>
> William
>
> William Miller
> Miller Solar
> Voice :805-438-5600 <tel:805-438-5600>
> email: william at millersolar.com <mailto:william at millersolar.com>
> http://millersolar.com
> <http://millersolar.com/>License No. C-10-773985
>
>