[RE-wrenches] AC Coupling Fronius IG Plus 10.0 inverter

Mark Frye markf at berkeleysolar.com
Wed Apr 13 13:47:27 PDT 2011


I see. Can this function be enabled/diabled?
 
Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 <http://www.berkeleysolar.com/> www.berkeleysolar.com  
 

  _____  

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of
Mark.Edmunds at schneider-electric.com
Sent: Wednesday, April 13, 2011 1:15 PM
To: RE-wrenches
Cc: re-wrenches-bounces at lists.re-wrenches.org; 'RE-wrenches'
Subject: Re: [RE-wrenches] AC Coupling Fronius IG Plus 10.0 inverter



Hi Mark, Gary, 

The Xantrex XW series inverters will  do a frequency shift to cause most
models of grid-tied inverter to disconnect when the batteries are full,
while the system is operating in an ac coupled off-grid mode. The following
app-note describes this operation. 

Cheers, 

Mark 

 
<http://www.global-download.schneider-electric.com/852577A4005D7372/all/8FA2
9D94B918A0FB8525781F0072FCA7/$File/ac-coupling-app-note(976-0240-01-01_rev-a
).pdf>
http://www.global-download.schneider-electric.com/852577A4005D7372/all/8FA29
D94B918A0FB8525781F0072FCA7/$File/ac-coupling-app-note(976-0240-01-01_rev-a)
.pdf
____________________________________________________________________________
_________ 

Mark Edmunds, P.Eng.  |   Schneider Electric   |  Renewable Energies
Business  |   CANADA  |   Director - Advanced Engineering 
Phone: +1-604-422-2609  |   Fax: +1-604-420-1591  |   Mobile:
+1-604-613-3285 
Email:  <mailto:mark.edmunds at schneider-electric.com>
mark.edmunds at schneider-electric.com  |   Site: <http:///>
www.schneider-electric.com/renewable-energies   |   Address: 8999 Nelson
Way, Burnaby, BC, V5A 4B5, Canada 

*** Please consider the environment before printing this e-mail 




From: 	"Mark Frye" <markf at berkeleysolar.com> 

To: 	<Gary at IcarusSolarServices.com>, "'RE-wrenches'"
<re-wrenches at lists.re-wrenches.org> 

Date: 	04/12/2011 09:37 PM 

Subject: 	Re: [RE-wrenches] AC Coupling Fronius IG Plus 10.0 inverter 

Sent by: 	re-wrenches-bounces at lists.re-wrenches.org

  _____  




Gary, 
  
I have been looking at some AC coupled stuff lately. The "FSC" is
propriatary to SMA, Sunny Island to Sunny Boy.  Pretty much anything else
you need something to sense the voltage of the battery bank so you can open
a contactor on the AC line to the Fronius when the battery voltage gets too
high. Once the voltage drops the contactor can close and bring the Fronius
back on line and then the 5-minute start up delay before it is feeding the
line again. 

Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 <http://www.berkeleysolar.com/> www.berkeleysolar.com   
  


  _____  

From: re-wrenches-bounces at lists.re-wrenches.org [
<mailto:re-wrenches-bounces at lists.re-wrenches.org>
mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Gary Willett
Sent: Tuesday, April 12, 2011 8:35 PM
To: re-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] AC Coupling Fronius IG Plus 10.0 inverter

Working on a proposal to add battery backup and a generator to an existing
10kW grid-tie system using the Fronius IG Plus 10.0 inverter.

Does anyone have any experience AC coupling this inverter to a Sunny Island
5048, or a Xantrex 6048? Is the Fronius capable of Frequency Shift control
(FSC) that comes from the battery-connected inverter?

Any other suggested solutions is appreciated. 

Gary Willett, PE
Icarus Solar Services LLC
 <mailto:Gary at IcarusSolarServices.com> 


______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
____________________________________________________________________________
_________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
 <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110413/717f1afa/attachment-0003.html>


More information about the RE-wrenches mailing list