[RE-wrenches] Can I handle the voltage drop?
Nick Soleil
nicksoleilsolar at yahoo.com
Tue Feb 15 10:00:50 PST 2011
Hi Mark:
I wouldn't feel comfortable with that scenario, either. Many inverters do
shut off at 254V-255V, but most of them can be adjusted if you have the software
and laptop for the job. Enphase generally shuts off when the AC voltage reaches
258V-259V. Keep in mind that just the Enphase cabling can add an additional
1.75% to the rise. I break my Enphase circuits into two sub-circuits of half
length.
Enphase is defintitely more tolerant of voltage issues than other
inverters. Xantrex is the worst, but can be adjusted.
Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037
________________________________
From: Mark Frye <markf at berkeleysolar.com>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Mon, February 14, 2011 7:42:11 PM
Subject: [RE-wrenches] Can I handle the voltage drop?
Can I handle the voltage drop?
Folks,
I am working on a proposal. It's a ground mount 300+ feet from the meter. There
is an existing, near by run of #2 copper I can tap into. The desired system is
relatively large, 64 amps AC max. I have modeled the yield using PV watts hourly
data, applying a power loss based on the voltage drop at the varying current.
This model shows a 3% loss in annual yield with the #2 copper. Because of the
economics of the system, we can absorb this loss.
My concern however is that I do not want the inverters to shut down when
operating at higher currents. I do not want a high AC line voltage fault due to
the voltage drop on the line. At the 64 amps max, the drop would be about 4%.
Of course all the manufactures I talk with recommend keeping the drop on the AC
below 1.5%.
I am looking at using Enphase inverters which spec an AC voltage range up to
264V, or 10% above 240V nominal.
What experience have folks had out there? How far can one realistically push the
1.5% limit and still avoid AC voltage faults when there is high voltage drop on
the line?
My guess is that everything would work out fine, but I stand to loss a huge
amount of energy if the inverters are spending all their time faulting and
resetting during daily peaks.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110215/eac78870/attachment-0003.html>
More information about the RE-wrenches
mailing list