By the way, in answer to answer your original question, capacitors of proper value, when installed in a circuit containing inductive loads, are capable of allowing the circuit to attain a power factor of 1.0.  As part of our Underwriter's Laboratories testing for our grid-tied inverters, a test fixture is used that's capable of both inductive and capacitive reactance (it's part of the anti-islanding tests).  I've witnessed the power factor being adjusted from 0.7 leading and lagging to an absolute perfect 1.0000 (yes, four decimals).  It's all done by varying the value of capacitance in the circuit.  Thus, if one were to use lab-grade test equipment, and take the time needed to make such a precision adjustment, it's possible to achieve absolute unity in an inductive circuit by "tuning" it with a capacitive circuit.


Dan
  

--- On Mon, 1/10/11, North Texas Renewable Energy Inc <ntrei at 1scom.net> wrote:

From: North Texas Renewable Energy Inc <ntrei at 1scom.net>
Subject: Re: [RE-wrenches] Xslent?
To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Date: Monday, January 10, 2011, 8:29 AM



 
How efficient is a 
capacitor in offsetting the power factor error? 99.9%...  ±2%...?
Jim 
Duncan

  -----Original Message-----
From: 
  re-wrenches-bounces at lists.re-wrenches.org 
  [mailto:re-wrenches-bounces at lists.re-wrenches.org]On Behalf Of 
  Exeltech
Sent: Sunday, January 09, 2011 9:03 PM
To: 
  RE-wrenches
Subject: Re: [RE-wrenches] Xslent?


  
    
    
      --- On Fri, 1/7/11, Peter Parrish 
        <peter.parrish at calsolareng.com>  wrote:


        > What ever 
        is done to reduce the reative power, it has to be done
        > in real 
        time (with a fraction of 0.016 seconds, the 60 Hz 
        cycle).
        > You can’t 
        wait until later in the evening to solve a problem 
that
        > is 
        occuring during the day.
        

        Peter is absolutely correct.  Power 
        factor correction MUST occur on a half-cycle by half-cycle basis, and at 
        the exact moment of power consumption by the reactive load.  
        Anything else won't be effective, and may in fact worsen the power 
        factor at a given point in the grid. 

        

         
        > Real time 
        compensation can be often done with capacitors alone
        > or in 
        conjuction with some smart electronics. Remember that 
        for
        > short 
        periods of time capacitors can store considerable 
        amounts
        > of energy 
        and can smooth out these reactive currents.
         
        
Capacitors placed across a power line will store 
        energy for exactly one-half cycle.  At that point, the polarity 
        reverses, the capacitor is discharged to to zero, then recharged to the 
        opposite polarity.  This process repeats every cycle.

What 
        DOES take place is a phase shift (displacement) in the current flow 
        relative to the voltage waveform.  Power factor correction is done 
        with capacitor banks (we see them in substations and on power poles) to 
        offset the power factor of the grid itself, which by its design is 
        inherently inductive due to long runs of wire.  Very large motors 
        will have individual "tuning" capacitors installed to offset inductive 
        reactive current flow.  These capacitors are disconnected whenever 
        the respective motor to which they're connected is not in use.  On 
        occasion, excessive capacitance exists in a circuit that must be offset 
        by inductance, but this is rare.


Like Tom Cruise said in Top 
        Gun .. "It's complicated."


Dan




--- On 
        Fri, 1/7/11, Peter Parrish 
        <peter.parrish at calsolareng.com> wrote:

        
From: 
          Peter Parrish <peter.parrish at calsolareng.com>
Subject: Re: 
          [RE-wrenches] Xslent?
To: "'RE-wrenches'" 
          <re-wrenches at lists.re-wrenches.org>
Date: Friday, January 7, 
          2011, 5:39 PM


          
          



          
          I know only a 
          little about Power Factor “charges”, but we can figure out some other 
          “engineering” issues.
          
           
          Power Factor 
          is a measure of the amount of reactive (out-of-phase) power compared 
          to real (in-phase) power. It is somewhat complicated but the PF is 
          unity for 100% in phase and 0 for 100% out-of-phase power. 
          
           
          The important 
          thing to remember is that (while holding the real power constant) for 
          PFs less than unity there is in addition to the real power, and 
          “in-flow” of power and an “outflow” of power four times a cycle. One 
          might say, “Why do I care about reactive power? It flows in and out 
          with no net contribution over the long run!). True, but the in-flow 
          and out-flow represents higher currents on the lines and 
          more  losses. Or it means that there have to be 
          oversized service conductors to avoid the extra losses. Even if the 
          losses are avoided, the higher currents can trip overcurrent 
          protection devices, and of course the utility company needs to supply 
          (and take back) the extra currents in real time.
           
          What ever is 
          done to reduce the reative power, it has to be done in real time (with 
          a fraction of 0.016 seconds, the 60 Hz cycle). You can’t wait until 
          later in the evening to solve a problem that is occuring during the 
          day.
           
          Real time 
          compensation can be often done with capacitors alone or in conjuction 
          with some smart electronics. Remember that for short periods of time 
          capacitors can store considerable amounts of energy and can smooth out 
          these reactive currents.
           
          I can well 
          imagine how an inverter can be designed to generate both real and 
          reactive power, and therfore an inverter can reduce the amount of 
          reactive power that needs to be supplied by the utility company – but 
          not when the sun isn’t shining. I suspect that these types of 
          inverters will have oversized output circuit wiring to handle the 
          reactive currents without adversely impacting their efficiency rating. 
          
           
          If I have 
          time this weekend, I will take a look at Apparent’s 
          website.
           - Peter
          Peter T. 
          Parrish, Ph.D., President
California Solar Engineering, Inc.
820 
          Cynthia Ave. , Los Angeles , CA 90065
CA Lic. 854779, NABCEP Cert. 
          031806-26
peter.parrish at calsolareng.com  
          
Ph 323-258-8883, Mobile 323-839-6108, Fax 
          323-258-8885                                                                                                   
           
          
          
          
          
          From: 
          re-wrenches-bounces at lists.re-wrenches.org 
          [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jamie 
          Johnson
Sent: Friday, 
          January 07, 2011 2:03 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Xslent?
           
          
          It's an 
          interesting product for a niche market if it actually works as 
          they say (Disclaimer:I am not 
          claiming that it does), after speaking with an individual who 
          I believe is the VP of Production for Apparent (use to work 
          for EnPhase according to their 
          website), he claims that the product is currently installed at 
          the Google campus on a solar canopy for some of their EV 
          chargers (can anyone verify this?)
          
           
          
          They have 
          several other beta installs as well, however the individual I 
          spoke to said they were only installing small systems at beta 
          test sites (where the Util co charges for VAR's using 
          separate meters like for EV charging) for now.  No 
          pricing has been set for the inverters, and they are not available for 
          sale to installers yet.
          
           
          
          Apparently 
          they claim the inverter can create/produce VAR's by taking 1 
          watt of power from the grid at night or from the solar output during 
          the day and turning it into approximately 9 VAR's to offset the 
          customers charges for VAR usage from the Grid.  This is 
          where the KVAh production on 
          the graph before sunrise and after sunset comes 
          from.
          
           
          
          I still 
          would need to see a third party head to head comparison test before I 
          believed it.  Again niche market inverter for when the 
          utility co charges for VAR's.
          
           
          
          Jamie
          
           
          
           
          
           
          
           
          
            
            -------- 
            Original Message --------
Subject: Re: [RE-wrenches] Xslent?
From: August Goers 
            <august at luminalt.com>
Date: 
            Fri, January 07, 2011 10:24 am
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>

Hi 
            All -

Thanks for the helpful info! We did a little more 
            research on our end and
I guess Apparent is the new brand name 
            for the Xslent product. 
            What
baffles me is the chart where they show that they're 
            producing power
before and after sunrise and sunset:

http://www.apparent.com/products/mgi.html

The 
            system must include batteries? Someone on their marketing team 
            is
really going to town...

Best, 
            August

-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] 
            On Behalf Of jay peltz
Sent: Thursday, January 
            06, 2011 4:43 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] 
            Xslent?

HI 
            Peter,

I agree with you that for now on residential it makes 
            no sense.
However for commercial that might have to pay extra for 
            PF issues, to have
the inverter adjust for this makes 
            sense.
Its the reason they( inverter companies ) are doing 
            it.
I"ve heard a better 
            more complete reason of course from Bill Brooks, who
maybe can 
            chime in.

sorry got away from me,


jay
peltz power
On Jan 6, 2011, at 
            2:34 PM, Peter Parrish wrote:

> I can't understand how any 
            inverter WOULDN'T deliver its power with the
> voltage and 
            current 100% IN PHASE.
>
> When the voltage and current 
            are not 100% in-phase that represents
reactive
> power. 
            Reactive power flows positive for a quarter of the AC cycle, 
            then
> negative for a quarter of a cycle, then positive and 
            then negative. The
net
> result over one AC cycle is ZERO 
            power delivered to the load.
>
> So reactive power is 
            worthless.
>
> Worse, it results in higher currents (and 
            voltages) for the same amount
of
> in-phase power, putting 
            additional stress on circuits.
>
> - 
            Peter
>
>
> Peter T. Parrish, Ph.D., 
            President
> California Solar Engineering, Inc.
> 820 
            Cynthia Ave. , Los Angeles , CA 90065
> CA Lic. 854779, NABCEP Cert. 
            031806-26
> peter.parrish at calsolareng.com
> 
            Ph 323-258-8883, Mobile 323-839-6108, Fax 
            323-258-8885
>

_______________________________________________

_______________________________________________
-----Inline 
          Attachment Follows-----


          _______________________________________________
List 
          sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options 
          & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
          http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List 
          rules & 
          etiquette:
www.re-wrenches.org/etiquette.htm

Check out 
          participant 
        bios:
www.members.re-wrenches.org



-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




      
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20110110/93f5720d/attachment-0003.html>


More information about the RE-wrenches mailing list