Phil, Mick and everyone else that replied:
Thanks. Great advice and I really appreciate all of you.
William Miller
At 10:03 PM 12/22/2010, you wrote:
>This was one of the limitations of the SW. If you want to have an EQ where
>the generator shuts off when its finished, you need to do a little trick.
>Setting the cursor to EQ just means the system will perform an EQ the next
>time the genny runs, and that might be some random time in the future.
>Setting the cursor to EQ and manually starting the genny works sort of,
>but somebody has to stay around and babysit the system to manually turn
>the genny off once the charge is done. Not ideal.
>
>If you set the cursor to EQ and then temporarily adjust the two minute
>start voltage up to any voltage higher than actual current voltage, you'll
>get an auto-start. Since it was started under the inverter's command, it
>will turn off once the EQ is finished.
>
>Once the genny's running reset the two minute start voltage back to original.
>
>Phil Undercuffler