[RE-wrenches] Strawbale wall penetration
nickl at sierrasolar.com
nickl at sierrasolar.com
Fri Nov 19 12:52:20 PST 2010
Ditto what Phil and Bill said. Also, I've found that you must add a
few sizes larger on the diameter of the hole as the straw tends to
fill the gap as it's drilled. On a recent job we had to utilize a 2"
hole for 1.25" conduit and it still needed to be forced a bit.
Downward slope is great advice too. Luckily my customer did that by
mistake.
Have fun, Nick
On Nov 19, 2010, at 12:22 PM, Phil Undercuffler wrote:
> Having a fair bit of experience with bale, I ditto what Bill
> mentioned but I'll add a simple way that I discovered to getting
> the inside and outside holes to line up.
>
> Bale walls are seriously thick, so standard extension bits aren't
> long enough. I found taking a 2 or foot length of 3/8" rebar
> chucked into a half inch drill works nicely for boring a pilot hole
> all the way through the wall. Once you have the pilot hole, it's a
> simple matter of drilling out a hole large enough for your conduit
> on both sides of the wall. Either use a small bit to drill a
> series of holes around the perimeter and connect the dots with a
> cold chisel, or use a hole saw that you don't mind sacrificing on
> the plaster. You don't actually have to "drill" through the entire
> wall, as the straw can be pushed to the side. I usually spin the
> rebar in the hole while chunking it back and forth a few times to
> clear a path, then thread the conduit through the hole using the
> rebar as a guide to be able to find the hole on the other side. It
> really helps to have a second person on the other side, to help
> guide it in the final inches.
>
> Rebar as a drill bit also works great with adobe walls.
>
> If you do a lot of this, take a minute to grind down a flat spot on
> the end of the bar or it will tear up your drill chuck. Drill
> chucks can be spendy. Ask me how I know...
>
>
> Phil Undercuffler
>
>
>
> On Fri, Nov 19, 2010 at 11:27 AM, Bill Hoffer <sunengser at gmail.com>
> wrote:
> Benn
>
> I used PVC in the my bale walls with a Junction Box on both sides
> of the penetration to protect the penetration (Outside a must!).
> I used EMT for all my other wiring, but PVC seems better for an
> interior to exterior penetration where the heat conduction of the
> EMT may cause some damaging condensation towards the exterior of
> the bales. I used a hammer drill and concrete bits to get through
> my stucco, it is tough stuff. I used 2 " conduit so I had to make
> several smaller holes and knock it out by hand. I did not have
> rebar in my bales, but heavyduty 6x6 mesh to get through, as would
> be expected I never was able to hit the middle of the grid, I just
> had to cut and hack saw when I hit something, pays to have a
> sacrificial bit to find the metal. I then fashioned a home made
> bit out of the conduit and used that to get through the bales by
> hand. That went pretty easy and will allow you to locate the rebar
> without damaging an expensive bit . Hard part is lining up to get
> a good mark on the opposite side. I used foam to fill any gaps,
> replastered around the pipe and fitting and caulked really well to
> seal against water on the outside. I also located the JB on the
> outside of the building in a very protected area for additional
> security. Water and straw bales do not play well together! If
> anything I would favor a slight slope downward on the outside so if
> there is a leak it will not follow the pipe inward into the bales.
>
> Hope that helps!
>
> Bill
>
> On Fri, Nov 19, 2010 at 11:05 AM, benn kilburn
> <benn at daystarsolar.ca> wrote:
> Wrenches,
> Short of contacting the builder, i'm looking for your experiences,
> practices and "look-out's" for penetrating a strawbale exterior
> wall with conduit.
>
> For the project in question there is currently a teck cable from a
> wind gen entering the home by sharing a HRV vent opening that i
> want to fix (not my original system by the way) and i will also be
> adding another penetration for a PV array that i am relocating on
> the property. The original penetration for the PV was done properly
> but its not in an ideal location for the re-located array wiring.
>
> I'm wondering if it is as simple as using a hole saw extension to
> go thru the ~16" wall and use an LB/box on either side. I'm sure
> there is some framework and/or rebar supporting the bales, how do
> you locate/avoid these when there are no corners to measure from?
> (it is a round home)
> Any knowledge if PVC or EMT will react in anyway with the bales?
> I'm thinking that PVC would be best....?
>
> ... i am trying to contact the builder to address this, and also to
> ask a few choice questions regarding the wiring methods (he?) used
> in the original PV system set-up.
>
> Cheers,
> benn
>
> DayStar Renewable Energy Inc.
> benn at daystarsolar.ca
> 780-906-7807
> HAVE A SUNNY DAY
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
> wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
>
>
> --
> Bill Hoffer PE
> Sunergy Engineering Services PLLC
> 2504 Columbia Ave NW
> East Wenatchee WA 98802-3941
> SunEngSer at gmail.com (509)470-7762
> Cell(509)679-6165
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
> wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
> wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20101119/00dd47f3/attachment-0004.html>
More information about the RE-wrenches
mailing list