[RE-wrenches] Outback Charging Method
Mark Frye
markf at berkeleysolar.com
Thu Jul 15 20:40:53 PDT 2010
Jay,
I took your advice on removing the foam and vents and it did make a
significant difference in the available charging power.
Thanks for the tip.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_____
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Monday, June 21, 2010 2:05 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Outback Charging Method
HI Mark,
I can't speak to the issue OB tech says here, although it doesn't seem to
support what I see in the real world.
One issue I have seen a lot of is the inverters getting hot, and then
derating the current output. I especially see this with them mounted in the
normal outback model. In a side by side mounting ( Midnite or custom) they
run much cooler.
In the past I have actually taken out the foam filter and side screens (when
I don't have to worry about debris getting into the inverters) and this has
both increased air flow substantially and also the charging rate for systems
with large batteries and generators that run for many hours at high charge
rates.
Hope this helps,
jay
Peltz power
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20100715/867ebd62/attachment-0004.html>
More information about the RE-wrenches
mailing list