[RE-wrenches] Supply Side Tap Overcurrent Protection

Steven Lawrence SLawrence at smartenergygroup.net
Wed Mar 31 13:19:32 PDT 2010


Hans,

There's a backup load panel that some house loads are transferred to that's fed from the 60A line side tap.  Under normal operation they are fed from the PV with the remaining power coming from the line side tap off from grid.  To be thorough, one would have to make sure that the backup loads aren't over 60A, and what's left in the main service panel wouldn't be over 60A.  But yeah, it always depends on the AHJ.

Here in NJ I try to stay away from panel upgrades whenever possible.  They can run from $2k-$3k, and that's not an adder I want to put on a client.  

Steven Lawrence


Date: Wed, 31 Mar 2010 11:39:32 -0700
From: "Hans Frederickson" <hans at fredelectric.com>
To: "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection
Message-ID: <3EE2AF007F5D4EBE96831C2254B5E83C at frederickson.local>
Content-Type: text/plain;	charset="us-ascii"

Steven,
I don't think the 60A disconnect for the line-side tap would qualify as part
of the required 100A rating for the residential service. You aren't using it
to supply the house loads. Unless I'm missing something, your proposal
limits the residential service load to only 60A. I suppose you could argue
it with the AHJ... but I think you're going against the intent of the code.
These sections weren't written with any consideration to grid-tied PV
feed-ins.

-Hans Frederickson

-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Steven
Lawrence
Sent: Wednesday, March 31, 2010 11:04 AM
To: re-wrenches at lists.re-wrenches.org
Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

230.80

"Where the service disconnecting means consists of more than one switch or
circuit breaker, as permitted by 230.71, the combined ratings of all the
switches or circuit breakers used shall not be less than the rating required
by 230.79"