[RE-wrenches] Supply Side Tap Overcurrent Protection
Hans Frederickson
hans at fredelectric.com
Wed Mar 31 10:24:17 PDT 2010
Anything less than a 100A main is a no-go a for residential service:
NEC 230.79(C):
"For a one-family dwelling, the service disconnecting means shall have a
rating of not less than 100 amperes, 3-wire."
Also, I don't think any AHJ is going to accept a load calculation in lieu of
proper bus sizing in the service. What's to stop the owner from adding loads
later on? I agree with Eric... time for a service upgrade.
-Hans Frederickson
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Steven
Lawrence
Sent: Wednesday, March 31, 2010 9:54 AM
To: re-wrenches at lists.re-wrenches.org
Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection
Why can't you do a line side tap and downsize the main breaker? Use a 60A
main disconnect for the line side tap, and use a 60A main breaker for the
service panel. That's similar to what I did except I downsized the 200A
main to a 150A. This also allowed a manual interlock kit in the main service
panel that can be fed from the backup load panel.
Steven Lawrence
______________________________________________________
Date: Wed, 31 Mar 2010 08:13:10 -0700 (PDT)
From: Nick Soleil <nicksoleilsolar at yahoo.com>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection
Message-ID: <342120.66732.qm at web44904.mail.sp1.yahoo.com>
Content-Type: text/plain; charset="us-ascii"
Downsize the main breaker? I would if I could, but the customer only
has 100 Amps now, and the solar is fed with two breakers, a 30A and a 40A.
So to be under 120Amps, I would have to size the main to 50 Amps, which may
be problematic.
I can also do the line side tap, but had heard that a load analysis may
be accepted instead. The loads of the house will never use more than 100
Amps. I am wondering if any codes or white papers detail that option.
Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC PO Box 657 Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
More information about the RE-wrenches
mailing list