[RE-wrenches] Supply Side Tap Overcurrent Protection
Steven Lawrence
SLawrence at smartenergygroup.net
Wed Mar 31 09:53:56 PDT 2010
Why can't you do a line side tap and downsize the main breaker? Use a 60A main disconnect for the line side tap, and use a 60A main breaker for the service panel. That's similar to what I did except I downsized the 200A main to a 150A. This also allowed a manual interlock kit in the main service panel that can be fed from the backup load panel.
Steven Lawrence
______________________________________________________
Date: Wed, 31 Mar 2010 08:13:10 -0700 (PDT)
From: Nick Soleil <nicksoleilsolar at yahoo.com>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection
Message-ID: <342120.66732.qm at web44904.mail.sp1.yahoo.com>
Content-Type: text/plain; charset="us-ascii"
Downsize the main breaker? I would if I could, but the customer only has 100 Amps now, and the solar is fed with two breakers, a 30A and a 40A. So to be under 120Amps, I would have to size the main to 50 Amps, which may be problematic.
I can also do the line side tap, but had heard that a load analysis may be accepted instead. The loads of the house will never use more than 100 Amps. I am wondering if any codes or white papers detail that option.
Nick Soleil