Does this mean the pole has to be galvanized? or depainted? I know you can not use coated rebar
Darryl
--- On Sat, 3/13/10, William Miller <william at millersolar.com> wrote:
> From: William Miller <william at millersolar.com>
> Subject: Re: [RE-wrenches] rebar v/s fiber
> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> Date: Saturday, March 13, 2010, 3:53 PM
>
>
> Ray:
>
>
> We've been using this interpretation for years.
>
>
> William Miller
>
>
>
>
> At 01:26 PM 3/13/2010, you wrote:
>
> Actually my read
> of 2008 code
> should allow the pole to qualify as the grounding
> electrode:
>
> 690.47 (D) allows the mounting structure to be the
> electrode if it
> meets 250.52.
>
> 250.52(A.7) plate electrode says you need at least 2 sq. ft
> of 1/4"
> steel plate.
>
> A 6" diam pipe 4 ft in the ground, will have 6.8 sq.
> ft of surface
> area......
>
> A 4" diam pole will have 4.7 sq ft of surface
> area.....
>
> Anybody see a flaw in this logic?
>
>
> R. Walters
>
> ray at solarray.com
>
> Solar Engineer
>
>
>
>
> -----Inline Attachment Follows-----
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-wrenches
mailing list