[RE-wrenches] Battery Cable REvistied
Glenn Burt
glenn.burt at glbcc.com
Mon Nov 29 18:03:03 PST 2010
Hi Ray,
I have for my last 2 battery jobs used the Cobra X-Flex in 2/0 size with MTW
rating.
At the battery end I have found the Thomas & Betts 54163-TB lugs, available
at my local Grainger store to be a good match both mechanically and
specification wise (also the correct hole size for M8 terminals in my
Concorde AGM's).
On the usual electrical equipment end, I use a Greaves Shoo-Pin PT131FX20 as
the appropriate reducer to a THHN stranding #2/0 size (available through our
local Graybar store, drop shipped to my office). Because I am using a Sunny
Island, of course nothing #2 fits. so I have two Polaris style connectors in
the trough below the SI where I switch from the Shoo-Pins to four #1 THHN to
go up into the SI batt terminals (two conductors per pole).
In fact, I am wrapping up one of these installs right now.
Don't know if this helps,
-Glenn
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of R Ray
Walters
Sent: Monday, November 29, 2010 11:58 AM
To: RE-wrenches
Subject: [RE-wrenches] Battery Cable REvistied
HI All;
I have struggled for years to get the right battery cable; in the old, old
days we used welding cable, which was better than THHN, but not with the
AHJs.
Then we used a SAE battery cable with 532 strands that was ideal, but not UL
listed.
Next we used Cobra X flex, but at over 2000 strands, we had the problem it
wasn't rated for some of the mechanical lugs and breakers. (too fine a
stranding)
Now I've found what I think is the perfect cable: Cobra Cop Flex, class I.
http://cobrawire.com/copflex/class_i.php
It's UL listed RHH, RHW , but is coarser stranded 532 strands, but not as
coarse as standard THHN (19 strands).
What do you guys think? RHH, RHW meets the code, with the coarser stranding
not being a problem with regular lugs, but still way more flexible than
THHN.
We're saved right?
R. Walters
ray at solarray.com
Solar Engineer
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20101129/2b735aaa/attachment-0003.html>
More information about the RE-wrenches
mailing list