[RE-wrenches] Tranformless inverter
Bill Brooks
billbrooks7 at yahoo.com
Fri Oct 1 11:36:36 PDT 2010
It has to do with the development of a “double-insulated” conductor needed for ungrounded systems. PV Wire is double-insulated while USE-2 is not tested as double insulated. It is analogous to double-insulated tools in the U.S. that do not require a ground wire.
Bill.
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Marco Mangelsdorf
Sent: Friday, October 01, 2010 11:09 AM
To: 'RE-wrenches'
Subject: [RE-wrenches] Tranformless inverter
Bill B. wrote the following:
Ungrounding the array requires additional fusing and disconnects, but the most significant difference is that the module wiring and all external cable must be PV Wire/Cable. Therefore only modules with PV Wire/Cable can be used in these systems. You must confirm from the manufacturer that they have made the switch. Hopefully all manufacturers will be installing PV Wire/Cable soon so that this will not be a problem anymore.
--My question: why is the standard USE-2 wire not acceptable any mo’?
marco
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20101001/96695083/attachment-0003.html>
More information about the RE-wrenches
mailing list