[RE-wrenches] Accessable?

Dave Click daveclick at fsec.ucf.edu
Wed Sep 15 09:28:49 PDT 2010


And more specifically:
690.34 Access to Boxes.
Junction, pull, and outlet boxes located behind modules or panels shall 
be so installed that the wiring contained in them can be rendered 
accessible directly or by displacement of a module(s) or panel(s) 
secured by removable fasteners and connected by a flexible wiring system.

Andrew Truitt wrote:
>
>
> Benn - I like installing j-boxes under the array as a general rule both
> for aesthetics and to keep them somewhat sheltered from the elements.  I
> do not see any code issues with the location because, as you mention,
> they are still accessible.
>
>
>  From NEC2008 Article 100:
>
> *Accessible (as applied to equipment)*. Admitting close
> approach; not guarded by locked doors, elevation, or other
> effective means.
>
> *Accessible (as applied to wiring methods)*. Capable of
> being removed or exposed without damaging the building
> structure or finish or not permanently closed in by the structure
> or finish of the building.
>
>
>
> - Andrew
>
>
>
>
> On Wed, Sep 15, 2010 at 3:15 AM, benn kilburn <benn at daystarsolar.ca
> <mailto:benn at daystarsolar.ca>> wrote:
>
>     Wrenches,
>     There has been some mention on this list lately of locating Soladeck
>     and/or other combiner boxes under arrays.  This has me wondering if
>     folks are doing this only for a cleaner looking roof array or if
>     there are other reasonable intentions (lack of available roof space).
>
>     Other than a cleaner look, i see no benefit to doing this. (don't
>     get me wrong, a cleanly installed array is something to be proud of)
>       However if the box ever needs to be accessed, you have to remove
>     at least one module to get to it, dealing with the whole 'breaking
>     the bond' issue; having to remove the module, replacing the WEEB
>     clip or undoing and then re-torquing the lug set screw,
>     re-installing module, etc.  If you just wanted to quickly check
>     something in the box (voltage, torque, whatever) it is no longer a
>     quick and easy task.
>
>     So the Canadian Electrical Code says in Section 0.....Definitions
>
>     _Accessible_ (as applied to equipment) - admitting close approach
>     because the equipment is not guarded by locked doors, elevation, or
>     other effective means.
>
>     _Accessible_ (as applied to wiring methods) -
>     (a) not permanently closed in by the structure or finish of the
>     building; and
>              (b) capable of being removed without disturbing the
>     building structure or finish.
>
>     My interpretation here is that;
>     (a) the box is not 'permanently closed in', just inconveniently
>     closed in. and,
>     (b) you are not disturbing the structure or finish, as you will be
>     replacing the module as soon as you are finished in the box.
>
>     Many pieces of equipment and/or panels require that you remove a
>     single piece or a multi-piece cover to access the wiring.  The pv
>     module is like a large 'cover' in this case. So i do not see this as
>     a code violation.  Do you?
>
>     I'm not familiar with the NEC, is it's definition of 'accessible'
>     similar to the CEC's?
>
>     Is this combiner mounting location under the array common practice
>     for some of you, or only done when roof space for a combiner box is
>     limited?
>
>     I am going to run this scenario by one of our inspectors, i just
>     thought i'd get some feedback from other Wrenches first.
>
>     cheers,
>     benn
>     DayStar Renewable Energy Inc.
>     benn at daystarsolar.ca <mailto:benn at daystarsolar.ca>
>     780-906-7807
>     HAVE A SUNNY DAY
>
>
>
>     _______________________________________________
>     List sponsored by Home Power magazine
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Options & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     List-Archive:
>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
>
> --
> "Don't get me wrong: I love nuclear energy! It's just that I prefer
> fusion to fission. And it just so happens that there's an enormous
> fusion reactor safely banked a few million miles from us. It delivers
> more than we could ever use in just about 8 minutes. And it's wireless!"
>
> ~William McDonough
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options&  settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules&  etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>



More information about the RE-wrenches mailing list