[RE-wrenches] The Demise of WEEB
William Miller
william at millersolar.com
Mon Sep 13 22:52:02 PDT 2010
Andrew:
You make a very good point in 2) below, however there is one step
missing: If a ground fault is occurring, the technician will eventually
need to look under modules to find the fault. This is the reason the
top-down clips will be loosened. If the module is grounded with #6 wire,
the wire will prevent the module from being lifted. Therefore, the lug
will also be loosened, un-grounding the module -- creating the unsafe
condition you described.
WEEB clip or WEEB lug, the technician dies.
Should we invent a WEEB jumper cable to maintain module bond while the
modules are being lifted?
William Miller
At 07:44 PM 9/13/2010, you wrote:
>2) My biggest concern with the WEEB Clip is that the moment a top-clamp is
>loosened the module is no longer grounded!!! To me that is not a good
>grounding method. Mr Wiley is obviously a talented inventor and he makes
>a strong argument for the quality of the bond that the WEEB Clip provides
>when the clip is installed properly and all mounting hardware is properly
>torqued. What I don't understand is the argument that this is as safe of
>a product as a properly installed outdoor rated lug for the service tech
>who has to work on that array.
>
>
>A tin-plated copper lug with a stainless steel set screw will last. A
>service tech working on a faulted array that was grounded with WEEB Clips
>might not.
>
>
>
>Andrew Truitt
>Free agent
>Golden, CO.
>